Your Open-Source Fire Sprinkler Spec - Part I

5/1/2024

 
One of the frustrating aspects of bidding a fire sprinkler job in North America is when you're reviewing a job and the specifications that accompany it are simply terrible - boilerplate, don't actually provide any useful information, are conflicting, include irrelevant content, or clearly haven't been updated in decades (list no longer manufactured products).

One of the ideas we kicked around a couple weeks ago was essentially an "open source" specification. One that we build and curate together and post for open use.

This is the first-stab at what "Part I" of an open, basic fire sprinkler specification might look like.

SECTION I OF THREE
Typical specifications include three parts:
  1. Conditions: where the scope is described, applicable criteria is communicated, and the 'what is supposed to be done' is addressed.
  2. Equipment: what equipment and products are permitted, and what are not.
  3. Execution: in what ways must the work be performed.

OUR GOAL
From our collaborations, posts and discussions thus far, we're all really wanting something that is:
  1. Helpful: actually provides information the contractor is needing to price a job.
  2. Concise: as short as possible, so that it's easier to read and easier to edit. Don't duplicate requirements from other standards (such as NFPA 13), but simply defer back to them. We also want to limit the number of sections (again for simplicity, easy to navigate).
  3. Clear: the specifications need to be easy to navigate and explicit in what is being required.
  4. Timely: we don't want antiquated methods or products that aren't feasible or achievable.

There are other goals too, but those seem to be the reoccurring themes.

We explicitly do not intend for this specification to replace consultant's who already update and care for the industry. The beauty of consulting is providing unique value to your clients - this is absolutely not intended to be the only specification available. 

Rather, we would hope that it could help provide a baseline open-source template where specifications could at least be of this quality level.

YOUR INPUT
Where we could really use help here is reviewing this initial (very very first) attempt at Part I a basic open spec. 

I have highlighted GREEN and BLUE areas where a specific selection needs to be made (one or the other).

I have highlighted YELLOW additional alternatives which may be less common than a typical, mid-size commercial job.

​All portions of this specification would be editable, though the highlighted areas would be of particular concern to change and update job-to-job.

Take a look, and let us know your thoughts. If you've been long-frustrated about the prevalence of terrible specifications - then this just might be your opportunity to help us clean up the practice:
Picture

Part II, which comes next, identifies equipment and products that are allowed or not.

Part III speaks to the execution of the work - that is, any restrictions on what needs to be achieved.

THANK YOU
Just want to say a big thank you in advance for helping us really impact the industry in a positive way. I and many others very much appreciate it!

​- Joe
James Art, FPE
5/1/2024 01:33:54 pm

Review and Inspection of systems can make a difference.

A huge fire loss that I investigated was a fire at a US Post Office distribution facility in Richmond, Ca.

They had a 10 year old 100 foot x 100 foot, 45 foot tall, sheet metal warehouse Addition to an older sprinklered three block long building, filled with mail sorting equipment.

The Addition had 40 foot tall rack storage of plastics, including plastic bins, and duffel bags made of synthetic fabrics, used mostly in their busy season in December.
The fire burned the Addition to the ground, and extended into the adjacent building, five rows of fire sprinklers in.

They had a mezzanine in the existing building, and there they had every piece of correspondence about the addition, including the Mechanical Engineer's bid documents.
The sprinkler plan consisted of just a floor plan of the addition,
with a large "X" over it, and in the middle, it said:
"Provide fire sprinklers to Ordinary Hazard."

The contractor did just that, and calculated to the existing fire pump.
Not only was the design not adequate, but the fire pump had been compromised.

The riser was left standing.
There was a water flow switch, but it had never had any wires attached.
Because this was a government facility, they did not have local permits, or need local inspections.
The government is "self insured", which as a practical matter meant Uninsured.

Chris Miller
5/1/2024 05:06:43 pm

I am excited to contribute to this......Lets start at the basic example given.....you indicated wet, dry, pre-action and deluge all in 21 13 13. In general, I prefer that instead of the 4 sections (16,19 etc) all with repeat structure. Since changing CSI is likely out of our influence, how can we structure 21 13 13 (my suggestion is use 21 13 13 for all wet systems) and just use the 16, 19, 21 etc for the 'special projects' that need special specific detail for organizational purposes. If you have a project with both wet, dry, and pre-action it could all be in 21 13 13 if standard nfpa 13 install. IF special direction is needed on the pre-action system outside of normal it would include 21 13 23 with a reference that in the 13 spec that points you to 23 and an note in the 23 spec that everything in 13 applies. If the work is outside of 13 (for example foam water 21 13 39 that is different NFPA standard) then it can stand alone as its own spec in every project.

Mitchell O'Bryant
5/2/2024 02:13:14 pm

Love this start! One comment I would add is to include the shop drawing/installation/etc. certification requirements under QUALITY ASSURANCE and then it can be removed from the submittal section. Would also recommend changing the language from "shall be signed by XXXX" to "shall be DESINED by XXX", NFPA 13 would carry the requirement to include designer quals on the shop drawings.

Moderator
5/8/2024 12:59:46 pm

We now have a PART 2 development - that's here: https://www.meyerfire.com/blog/an-open-spec-for-fire-sprinkler-systems-part-ii


Comments are closed.
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    AI
    Announcements
    Author Jocelyn Sarrantonio PE
    Book Review
    Calculators
    Career
    Course
    Delegated Design
    Design Challenge
    Detail Critique
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Opinion
    Passive Fire Protection
    PE Exam
    Perspective
    Pick A Part
    Pick-A-Part
    Products
    Site Updates
    Special Hazards
    Specifications
    Sprinkler Systems
    Standpipes
    Students
    Talks
    Tools
    Videos


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    January 2025
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT