Small Tweaks, Big Shifts: How Change Happens

10/25/2023

 
Earlier this week I needed to copy a four-unit apartment where I designed the 13R sprinkler system and simply roll it over into a new job.

It was a complete duplicate building, just in a different location (new jurisdiction, different water supply).

Slam dunk. Easy, done. Right?

Well sure, except then I looked at my prior layout. I couldn’t stand it. I looked at my own set of plans from just three years ago (2020!) and they look terrible.

Now, the actual layout was fine. The sprinkler, locations, pipe are fine. Plans are OK. They were not at a stage that I think the average person would look at them and puke – but when I look at them I want to.

Why?

There are so many different tweaks and improvements on the presentation in three years that the work I do today simply looks very little like the work I was doing just 36 months ago.

The titleblock is hard to read. When you look at the coversheet, it’s a mess of schedules and details and sections seemingly thrown around wherever they would fit. There’s no big bold title at the top, nor any kind of easy recognition on whether this project is on Main Street or Mars.

It’s disjointed, doesn’t flow, isn’t what I would choose to do today. I get little goosebumps now having to stare at it now.

IMPROVEMENT 
We don’t all stand on the shoulders of giants when we start out. We don’t hit perfection right off the bat.

In reality, we should acknowledge that we’re very clearly never operating in a state of perfection. There is always room for improvement.

And even if tradition says that our organization has done something the same way for 25 years, we need to be adapting to the needs of today and making use of the tools of today.

One single big overhaul that changes a whole organization’s work style and work output simply never happens. OK – maybe somewhere for somebody, a big, conscious overhaul of standardization and workflow is theoretically possible. But if it actually has happened somewhere, then it had to be exceptionally painful and surely not quick.

Improvement doesn’t happen ‘when we have time to take that on’. It happens in very very small increments. Micro improvements. A tweak here on this job. A nudge here on this job. A lightbulb on this job.

What worked better? What worked worse?

Adapt and move the chains forward. It’s far better in our world to take the 4-yard gain every single play than it is to throw 3 Hail Mary’s, fail, and then punt on the idea.
 
NO LIGHTNING-STRIKE CHANGES
If we tinker and tweak (surely I’m using some kind of Gen-Z curse word here or something?) things constantly, find what works, and adapt over time – that’s when we do actually make change happen.

We also don’t get this lightning-strike ideas all at once. We get lots of little ideas over time, that, when executed, add up.

It’s only after implementing all the constant little improvements that the big differences can start to show.

That’s why my gut sinks when I look at the presentation from a 2020 project.

It’s not one thing – it’s the 30 things that have all improved since then.

THANKS, JOE. 
Yes, I’m somewhat embarrassed of the work that happened not even that long ago.

But no, I didn’t come here today to brag about my own self-improvement.
 
SPINNING IT FORWARD
What I’m really interested in – is taking that look back and spinning it around.

Where do we want to be, as an organization, in the next three years?

Where do I want to be, as a person, in three years?

Where do we want to take the industry, in three years?

3-YEARS TO TEN? 
Where is it that we can take things? For me as a person, for my team, but also – what about all of us?
 
Three years seems hard enough to imagine. But carry out that thought – where can we all be, as an industry, in ten years?
 
Let’s set aside the news network hysteria and world ending predictions for just a second and assume that things are going to be mostly around in 2033.

That the fire protection industry will be growing and adapting just as it has for the last 120+ years.

What do we want the industry to be in 2033?

OVERESTIMATING THE SHORT GAME, UNDERESTIMATING THE LONG 
A famous person once said, “Most people overestimate what they can do in one year and underestimate what they can do in ten years.”

I find this to be slap-me-in-my-face true.

And I find the evidence for that easily when I look back on the last ten years.

What happened?

Where was I?

What did I know then?

What did I not know then? (answer: it was much more than what I knew)

What was I doing then?

What am I doing now?

2033 
In 2033, will we all be sitting around and griping about the same issues that we gripe about today?

Are we going to fix the issues surrounding delegated design? The boilerplate specs from 1985? Bid drawings that themselves obstruct code? Or perhaps just as important, the apathy some people have towards fire protection?

Is it still going to be a problem?
 
If not – what must happen?

How far away are we from changing the outcome?

Even if it is big – or would take a lot of effort, or resources, or awareness – is it not something that we couldn’t completely change by 2033?

THOUSAND SMALL INCREMENTS 
If we look back – see how all our small changes stack up – and then look back forward: it’s the thousand small increments that will make the big difference.

What are the small actionable items, today, that move us all in the right direction?

How do we break giant problems down so that we can hit the 4-yards of progress now instead of waiting for a Hail Mary in nine years?

What is that?

What does that look like?

TIME + PRESSURE 
I’ve spoken with enough people I admire that I believe in my core that there are few things we can’t solve given enough pressure and enough time. I see a path where we can change the trajectory of the industry if we choose to do so, collectively.

It all depends on what we choose to do today.

What will we etch in a small way today that keeps us moving towards big change tomorrow?

And without sounding like I’ve completely gone off the rails; I think about these things a lot. I feel extremely fortunate to be able to do so with the website and the content and community that hang around here. I am so thankful for that.
I don’t mean taking on big challenges in a figurative sense – I mean it as an actionable challenge.

If you’ve got a gripe with how our industry operates – what are you doing about it? What change can you make now that moves things in a better direction for all of us?

Around here we’ve got “irons in the fire” so to speak to be making progress towards the areas we really care about. Some things maybe awareness. Others education. Maybe resources. Maybe advocacy. 

Maybe they’re slow burns – maybe they won’t come to life for some time – but after lots and lots and lots of little victories maybe they will make it out to the world and make some real tangible change.
 
Ten years from now simply seems unfathomable for me to comprehend. Maybe it’s my age or my kids’ ages or that so much has changed in my world in the last decade. It’s difficult for me to picture it. I can only barely imagine what 2 years from now could look like.

But if you assume that 2033 will happen, that it will hit us at some point: will we be looking back and be mildly embarrassed by how things used to be – because so much has changed? Or will we gripe about the same issues without doing anything about it?
Eric R
10/25/2023 11:14:37 am

Joe, your first section here certainly hits home whenever I have to look back at plans, some way less than 3 years old even!

Taking a moment to flip through old drawings is certainly something I'd recommend any designer to do. Sure the cringe factor will be painful, but you are correct in that it provides a great way of showing growth that might otherwise go unappreciated.

Another great way as an installer is when I have to visit older projects for inspections or renovations and I get to experience how horrible I was at building sprinkler risers not that long ago.

Barry L
10/25/2023 11:16:58 am

Joe, you hit the nail on the head, sir. Great post!

Patrick Drumm
11/24/2023 11:51:55 am

"In 2033, will we all be sitting around and griping about the same issues that we gripe about today?"

Joe, the above question is so powerful. It is my hope that at that point we have fixed at least a few problems of today and are beginning to tackle new problems that are sure to develop. I believe if enough people get involved and somehow brainstorm/crowdsource/organize some real improvement could happen in our industry. A lot of people have good ideas out there but do not know how to implement them. This site is such an important tool not only for learning but communication between dedicated professionals.

Thank you for everything you and the community you have built is doing to help change the game!


Comments are closed.
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    AI
    Announcements
    Author Jocelyn Sarrantonio PE
    Book Review
    Calculators
    Career
    Course
    Delegated Design
    Design Challenge
    Detail Critique
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Opinion
    Passive Fire Protection
    PE Exam
    Perspective
    Pick A Part
    Pick-A-Part
    Products
    Site Updates
    Special Hazards
    Specifications
    Sprinkler Systems
    Standpipes
    Students
    Talks
    Tools
    Videos


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    January 2025
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT