Requirements for Fire Sprinklers at Ceiling Fans

12/5/2018

 
If you work with sprinkler systems & review layouts, you've undoubtedly encountered sprinklers near ceiling fans. Today I'm taking a look at some of the requirements for sprinklers near fans, and the basis for those requirements.

Traditional Ceiling Fans

​The chief concern with a typical residential-style ceiling fan is that the fan motor housing and fan blades could form an obstruction to proper sprinkler discharge.

Motor Housing Obstruction

NFPA 13 addresses the discharge from the motor housing by the Three Times Rule, where the sprinkler must be located three-times the width of the obstruction up to 24 inches (610 mm).

Fan Blade Obstruction

In terms of obstruction from the fan blades, NFPA 13 also allows sprinklers to be placed "without regard" to the blades of ceiling fans less than 60 inches (1.5 m) in diameter as long as the plan view is at least 50 percent open (NFPA 13 2010-19 under "Obstructions to Sprinkler Discharge Pattern Development" subsections in Chapter 8).

NFPA 13R 3 and 5-foot Rules

NFPA 13R takes a more straightforward requirement for positioning of sprinklers near ceiling fans - residential pendent sprinklers must be 3-feet and residential sidewalls must be 5-feet unless another sprinkler is positioned on the adjacent side, or, the sprinkler is positioned so that the fan is not considered an obstruction (NFPA 13R 2007 6.8.1.5.3, 2010-19 6.4.6).
​
Ceiling Fan Fire Sprinkler
Residential style sprinklers are impacted by ceiling-mounted obstructions, such as lights and fans, to a greater degree than obstructions down from the ceiling since residential sprinklers throw with more high-wall wetting
NFPA 13R Research Basis

The NFPA 13R guidance was driven by fire modeling, sprinkler response tests, distribution tests, and full-scale fire tests by the National Fire Sprinkler Association and the Viking Corporation in 2005 (Valentine and Isman, Interaction of Residential Sprinklers, Ceiling Fans and Similar Obstructions). These tests indicated that the fan blades where not significant obstructions as long as the sprinkler was far enough away from the motor housing, allowing the sprinkler to control a fire on the other side of the fan in a small room.

These tests also indicated that fans on low to medium speed did not significantly impact sprinkler performance, but high speed did. Despite the effect, the fire was still controlled in small rooms. Larger rooms, due to the size, would be expected to require additional sprinklers (NFPA 13R 2007 Annex).
High Volume Low Speed Fans (HVLS) 

Fans moving larger volumes of air can have a significant impact on plume development and fire sprinkler response.

In 2009, a research project sponsored by the Property Insurance Research Group (PIRG) and other industry groups, coordinated by the Fire Protection Research Foundation (FPRF) ran a series of 10 full-scale fire test and limited scale testing to evaluate the impact on sprinkler system performance. 

In 2011, a second phase was conducted by Factory Mutual Research Corporation.

Recommendations from Research

Based on the tests, effective sprinkler operation was obtained when the HVLS fans did not obstruct sprinkler discharge and were shut down upon the activation of the first sprinkler.

The research also included shutdown by air-sampling type detection and use of ionization type smoke detectors, with earlier fan shutdown resulting in less commodity damage. FM Global's recommendations even extend into smoke detection devices or heat detection devices as an acceptable means to conduct the fan shutdown (provided uniformly above the fan blade area, per Data Sheet 548).
Big Ass HVLS Fan with Fire Sprinklers
Due to size and large air movement, High Volume Low Speed Fans (such as Big Ass fans) impact sprinkler discharge as both a potential obstruction and as a large air mover

​NPFA 13 Requirements for HVLS Fans

NFPA 13 defines high volume low speed fans as ceiling fans approximately 6 feet (1.8 m) to 24 feet (7.3 m) in diameter, with a rotational speed of approximately 30 to 70 revolutions per minute (NFPA 13 2013-16 Section 3.3.14).

Beginning with the 2013 Edition of NFPA 13, NFPA 13 has required four principal items concerning these large fans (NFPA 13 2013-16 Section 11.1.7 and 12.1.4 for storage):
(1) The maximum fan diameter must be 24 feet (7.3 m)
(2) HVLS fans be centered approximately between four adjacent sprinklers
(3) The vertical clearance from the fan to the nearest sprinkler deflector must be a minimum of 3 feet (0.9 m)
(4) HVLS fans must shutdown (via interlock) immediately upon receiving a waterflow signal in accordance with NFPA 72.

While NFPA 13 suggests centering the fan between four sprinklers - trying to convince an architect or mechanical engineer to shift their equipment based on the sprinkler system can be difficult to do. I've had better success designing the sprinkler locations around the fan location.


Thoughts

Since sprinklers are designed to be sensitive to air temperature and movement, ceiling fans can impact performance. With small ceiling fans, the biggest concern is obstructing sprinkler discharge, while for larger HVLS fans this chief concern moves towards the movement of air and impacting the response. Fortunately, research-backed recommendations have been provided to still allow effective fire sprinkler protection alongside ceiling fans.

Subscribe

Want more like this? Get these free weekly articles here.
Dave L.
12/5/2018 03:17:00 pm

Great article, and timely - HVLS fans are becoming very popular; they aren’t just for cows anymore. I’m glad NFPA came up with a definition (sort of) for HVLS, the definitions out in the industry are fuzzy. The existence of HVLS fans (confirm that they are) can be hidden on the RCP, or in the mechanical drawings (pay particular attention to room such as gymnasiums and commons areas). Hopefully the design team scienced-it out ahead of time. The fans may or may not be designed to the proper distance below sprinklers, and throughout the job it is not uncommon for them to shift or change in quantity! Others may not be aware of the impact these small changes are on the sprinkler design. Coordinating with the fans during design is much better than having to react later.

Jess L.
3/7/2019 10:16:51 am

Thank you for compiling this information into one place!
I've often seen ceiling fans get overlooked in re: to sprinkler layout.
They sometimes are not shown on the architectural RCP's, but on the Interior design drawings!

Old Mate
7/30/2019 12:45:55 am

Very Cool

Neil Holden
3/16/2020 05:40:42 am

Great article. It summaries common sense very well in terms of fans


Comments are closed.
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    AI
    Announcements
    Author Jocelyn Sarrantonio PE
    Book Review
    Calculators
    Career
    Course
    Delegated Design
    Design Challenge
    Detail Critique
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Opinion
    Passive Fire Protection
    PE Exam
    Perspective
    Pick A Part
    Pick-A-Part
    Products
    Site Updates
    Special Hazards
    Specifications
    Sprinkler Systems
    Standpipes
    Students
    Talks
    Tools
    Videos


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    January 2025
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT