New Fire Hydrant Flow Test Charts (PDF)

7/14/2021

 
One of my wanted items on my personal to-do list was a full lineup of flow charts that incorporate discharge coefficients coming off a fire hydrant. These (in my line of work) are most commonly used in fire hydrant flow tests, where flow comes out of the side (commonly 2-1/2") outlets or the main pumper outlet (single 4" or larger).
Picture
So what is a discharge coefficient? 

When we flow out of an orifice, water is restricted and forced into a smaller cylindrical shape. The discharge coefficient is what helps us adjust the measured pitot pressure, which is taken along the centerline of the stream, and adjust for about how much flow is coming through the opening.

It's simply comparing the size of the actual stream against the size of the opening.

When a long straight stream-straightener is used, this coefficient is high. The stream is less tightly condensed as compared to the opening dimension.

When water takes a more difficult approach and is restricted in its flow, this coefficient is lower.
Picture
Picture
Picture
Discharge Coefficients as Identified in NFPA 291
We'll discuss this in more detail later. For today, we've created flow charts for these three different discharge coefficients. See the PDF link below to get access to all three flow charts, broken out across a number of different orifice sizes.
Picture
GET FLOW CHART PDFS
Thanks for being a subscriber and being part of our story. We're all about sharing helpful content and finding ways to support the industry by making you, the fire protection pro, shine. We hope information like this is helpful.

Thanks & have a great week!
Kevin LaRose
7/14/2021 01:51:59 pm

Thank you for this chart. I always apply the correct coefficient on my flow tests but I still don't understand why we would take the results from our flow test which is after the hydrant outlet and use a coefficient to make the results worse. Aren't our readings already worse than what we have available before the hydrant outlet?

Joe Meyer
7/14/2021 02:51:37 pm

I've thought about this quite a bit myself.

In the coefficients we are accounting for the method in how we are measuring the stream. If it were otherwise easier to measure flow, we could just fill up a 5,000 gallon tank exactly and time how long it takes. It either isn't consistent or isn't practical, so we take the pitot instead.

We are not factoring the loss through the pathways that the water takes to flow out of the hydrant. Usually, there would be a tee, and elbow up, and effectively a 90-degree turn that water has to take just to go from a city main to flow out the hydrant. We're not accounting for that here through this coefficient.

I'd want to do some more study/calcs to see how much we actually are losing due to how we test a hydrant (and not just a giant opening in the main itself). I would think if our flows are relatively low compared to the size of the pipe to the hydrant, then these effects are not huge. Not inconsequential, but not huge.

Brian Gerdwagen FPE
8/3/2021 02:45:25 pm

Do the larger diameter pumper outlets include the extra reducing coefficient per Table 4.8.2?

Joe Meyer
8/3/2021 03:02:50 pm

No - the pumper coefficient needs to be in ADDITION to the coefficients applied above.

Good clarification Brian.

David Kulbacki
9/22/2021 03:22:52 pm

In my area many designers use the main test/drain or one of the FDC inlets to conduct forward flow for the double check backflow assembly. They use the velocity pressure pitot equation to demonstrate that they will achieve the system demand flow. During the acceptance testing, I verify that the system demand is achieved by measuring with a pitot gauge and calculating the flow.

I generally use a coefficient of 1 when a hose monster or the main drain piping is flowed from, because they are long runs of smooth continuous pipe. Is this appropriate or should I be using some other coefficient?

Moderator
9/22/2021 03:24:46 pm

Great question David - we're going to throw this in the Forum queue as I think it'd be a good discussion point. Thanks for commenting!


Comments are closed.
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    AI
    Announcements
    Author Jocelyn Sarrantonio PE
    Book Review
    Calculators
    Career
    Course
    Delegated Design
    Design Challenge
    Detail Critique
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Opinion
    Passive Fire Protection
    PE Exam
    Perspective
    Pick A Part
    Pick-A-Part
    Products
    Site Updates
    Special Hazards
    Specifications
    Sprinkler Systems
    Standpipes
    Students
    Talks
    Tools
    Videos


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    January 2025
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT