Basic Open Fire Sprinkler Specification - Version 1

6/5/2024

 
First - thank you to all the feedback, comments, and emails that made this possible. This community of professionals looking to help improve the industry is second to none. 

I very much appreciate the time and input in building this together.

A BASIC, OPEN-SPECIFICATION CONCEPT
One of the frustrating aspects of bidding a fire sprinkler job in North America is when you're reviewing a job and the specifications that accompany it are simply terrible - boilerplate, don't actually provide any useful information, are conflicting, include irrelevant content, or clearly haven't been updated in decades (list no longer manufactured products).

One of the ideas we kicked around and now delivered is essentially an "open source" specification. One that we build and curate together and post for open use.

We 
explicitly do not intend for this specification to replace consultant's specs who already update and care for the industry. The beauty of consulting is providing unique value to your clients - this is absolutely not intended to be the only specification available. 

Rather, we would hope that it could help provide a baseline open-source template where specifications could at least be of this quality level.

OUR GOAL
From our collaborations, posts and discussions thus far, we're all really wanting something that is:
  1. Helpful: actually provides information the contractor is needing to price a job.
  2. Concise: as short as possible, so that it's easier to read and easier to edit. Don't duplicate requirements from other standards (such as NFPA 13), but simply defer back to them. We also want to limit the number of sections (again for simplicity, easy to navigate).
  3. Clear: the specifications need to be easy to navigate and explicit in what is being required.
  4. Timely: we don't want antiquated methods or products that aren't feasible or achievable.

There are other goals too, but those seem to be the reoccurring themes.

THE DOCUMENT
I have highlighted 
GREEN and BLUE areas where a specific selection needs to be made (one or the other).

I have highlighted YELLOW additional alternatives which may be less common than a typical, mid-size commercial job.

​All portions of this specification would be editable, though the highlighted areas would be of particular concern to change and update job-to-job.

DISCLAIMER
A very important note here, as is with all tools and resources for the fire protection space. Any information presented should not be relied upon as a replacement for sound engineering judgment. ​Use only at your own discretion. While we build these to help improve aspects of the industry, we are not and cannot be assume responsibility for use of the specification. For more on our Terms of Service, please visit: https://www.meyerfire.com/terms
Picture
    Visit https://www.meyerfire.com/terms.html for terms of use.
GET SPECIFICATION

Another big thanks to everyone who helped make this happen. If you're looking for a baseline set of specifications for comparison, for a basic project, or for a consultant who asks - we now have something to share.

Towards a better industry - thanks! 

​- Joe
Ray Hardy link
6/5/2024 10:36:55 am

Having trouble downloading it, which is a shame because I'm really looking forward to reading it.. great work Joe.

Joe Meyer
6/5/2024 10:38:09 am

Hi Ray - did you enter your email to get it?


Comments are closed.
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    AI
    Announcements
    Author Jocelyn Sarrantonio PE
    Book Review
    Calculators
    Career
    Course
    Delegated Design
    Design Challenge
    Detail Critique
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Opinion
    Passive Fire Protection
    PE Exam
    Perspective
    Pick A Part
    Pick-A-Part
    Products
    Site Updates
    Special Hazards
    Specifications
    Sprinkler Systems
    Standpipes
    Students
    Talks
    Tools
    Videos


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    January 2025
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT