Basic Components of a Dry Valve

8/22/2018

 
I've never trimmed a dry valve nor have I tested or drained a system myself. I'll also admit that for longer than I should have I never investigated the details of a dry valve.

Hopefully with today's post if you've been in that same boat there's enough to better understand the basic components of a dry pipe valve.

How Dry Pipe Valves Function
1. The valve is in the closed position (clapper inside the valve is horizontal) and air pressure keeps the clapper closed.
2. A sprinkler activates, releasing air pressure at the sprinkler.
3. Air pressure within the dry pipe system begins to reduce.
4. After sufficient air pressure is reduced, the water pressure below the clapper becomes greater than the pressure above the clapper, and the valve opens upward.
5. Water flows through the opening in the valve, past the clapper, and into the system.
6. After entering through the valve, the water gravitates towards the opening in the system where the air pressure is being released, and discharges through the sprinkler at the fire interface.

Dry Pipe Valve

Clapper Assembly
The clapper is the interface between the air and the water within a dry pipe valve.

It's purpose is to remain closed when air pressure is sufficient in the system, and open when the air pressure falls.

The surface area of the clapper is disproportionately larger on the air side than the water side - which is intentional. To hold the clapper closed, the force on the clapper must be greater on the air side than the water side. Since force is pressure x area, a larger surface area on the air side means the air can be kept at a much lower pressure and still keep the clapper assembly closed - often to a ratio of 4:1 or 5:1 (allowing 40 psi of air to 120 psi of water pressure, for instance). 

External Reset
The External Reset Knob shown in this model is used in lieu of priming water, which otherwise sits on top of the clapper and helps distribute pressure across the top interface of the clapper.

The Knob incorporated in this dry valve is depressed to "unlatch" an open clapper, allowing it to reset back into its normal, closed position. It is a convenient function where a user doesn't have to open the face of the valve in order to reset it.

Low Body Drain Valve
The low-body drain valve allows the air-side of the valve to be drained completely with the clapper closed. Since the main drain valve is below the clapper, the clapper must be opened for the main drain to be used to drain the system.

Main Drain & Intermediate Chamber

The main drain is used to drain water from the system, and is located below the clapper assembly.

For dry valves, some models permit the main drain to be used to test the waterflow pressure switch without opening the clapper.

In other models, there's an intermediate chamber between the water and air side which is normally dry. When water enters the intermediate chamber after the valve opens, the waterflow pressure switch senses water pressure and activates. In this configuration, there's usually a ball valve that can be used to test the waterflow pressure switch and fill the intermediate chamber without opening the dry valve.

Pressure Gauges
The water supply pressure gauge and the system air pressure gauge are included to monitor the incoming water supply pressure and the system air pressure. These gauges are usually attached to a gauge test valve with a plug that permits removal and cleaning of the gauge orifice.

​Pressure Switches
There are typically two pressure switches on the dry pipe valve assembly. The first is a pressure switch which monitors the air supply. When the air supply on the system drops to a pre-determined level, this pressure switch will typically send a supervisory signal to the fire alarm control panel, allowing an early warning that the dry valve is about to open and flood the system.

The second pressure switch is included to activate when there is water in the intermediate chamber or is flooding the system. This is typically an alarm signal that also activates fire alarm notification in a building.

Supply Shut-Off Valve
This valve is typically separate from the dry pipe valve, but allows the system to be shut off after a fire has been sufficiently suppressed. It also can be closed when a system needs to be isolated, such as for a modification, repair or remodel.

Other Items
Outside of the dry valve assembly, an air maintenance device allows the incoming air to be regulated to a preset air pressure and for that pressure to be maintained in the system.

In order to supply the air, or in many cases now nitrogen, an air compressor or nitrogen generator are provided to supply pressured air or nitrogen into the system.

Summary
While this valve is only one model, many of the components between dry valves are designed similarly. For further reading and detail on dry valves, I'd recommend reading NFSA's Layout, Detail and Calculation of Fire Sprinkler Systems (2nd Edition by Kenneth E. Isman, P.E.) and any product data for a dry valve you're reviewing, installing, or specifying.

Subscribe Today
Don't get these free weekly articles? Subscribe today and get a free PDF guide on Canopies & Overhangs.
FOLLOW THE CAUSE

Comments are closed.
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    AI
    Announcements
    Author Jocelyn Sarrantonio PE
    Book Review
    Calculators
    Career
    Course
    Delegated Design
    Design Challenge
    Detail Critique
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Opinion
    Passive Fire Protection
    PE Exam
    Perspective
    Pick A Part
    Pick-A-Part
    Products
    Site Updates
    Special Hazards
    Specifications
    Sprinkler Systems
    Standpipes
    Students
    Talks
    Tools
    Videos


    ARCHIVES

    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    January 2025
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT