A Calculated Study of Porte-Cochere Proximity

9/11/2019

 
Last week I discussed across a common misconception with porte-cochere sprinkler requirements and how code addresses sprinkler protection for these structures.

This week I’m diving a little deeper with some estimates of how a porte-cochere fire would actually affect a main building, based on distance from the building.

It’s important to note that this exercise is largely academic: with the calculations below I’m making some gross assumptions that overly simplify the situation. This has not been vetted with Ph.D. experts nor gone through full scale fire testing. I’m just running some basic numbers with big assumptions to illustrate a point.

Heat Transfer

From what science gives us - heat is transferred by three methods. Conduction, convection, and radiation.
Conduction is the transfer of heat by objects touching each other. The direction of transfer is dictated by hot-to-cooler materials in direct contact.

Convection is the transfer of heat caused by the movement of gas (or a fluid). The direction of transfer is largely dictated by overall movement of the fluid, and for smoke tends to be vertical.

Radiation is the transfer of heat from the emission of electromagnetic waves. The direction of transfer is in all directions, but can reflect and re-emit from other surfaces.

Heat Transfer for a Flame

For a flame, depending on the fuel, most of the heat will be transferred away from the flame source primarily by convection. The chemical reaction (oxidation) of a flame will cause gases to heat. The heated gas’ molecules will become more active and less dense. With less-dense gas than surrounding cooler air, the warm gas will rise up and away from the flame source and carry solid particles forming hot smoke.

Radiation will typically comprise 20-35% of the overall heat release rate for a fire. Radiation transfers heat from the source in all available directions until it contacts another surface. Once in contact with other surfaces, radiation can be absorbed or re-emitted from the surface, depending on the surface material.

Conduction is the least important mode of heat transfer in an open fire. Radiation near a flame’s origin, for example, often emits and heats up adjacent surfaces with more impact than conduction. For wall assemblies, conduction of heat through penetrations becomes important, but for flames in open environments conduction plays only a small role.

Three Porte Cochere Scenarios

100-foot Separation
Now imagine a porte-cochere that is 100 feet (30 m) from the face of a larger main building to the center of the porte-cochere. If the porte-cochere is completely inflamed, how would it transfer heat to the main building?

It would transfer heat only by radiation; and in very small amounts. Assumptions include a 5 megawatt (MW) fire from a wood-built porte-cochere, a 100-foot (30 m) center distance from the main building, an atmospheric transmissivity of 0.95, and a 30% of the overall heat loss as radiation.

Using the Lawson and Quintiere Point-Source Method, the incident radiant flux (a measure of the heat energy per area) is 0.13 kW/sqm.
Picture
 
This radiant flux is about 10% of the flux for a 1st degree burn on unprotected skin.

30-foot Separation
Now move the porte-cochere to be 30 feet from the face of the building. Radiation will again transfer heat to the face of the building, but in a much larger amount. Because radiant flux is related to the inverse square of the distance between the targets, this 30-foot distance will actually have a radiant heat flux 10 times greater than a porte-cochere fire 100 feet away. For the same size fire as before but at 30-feet, this could be about enough heat for a 1st degree burn.
​
Picture
At the 30-foot distance, however, heat transfer to the main building is still primarily by radiation. The hot, buoyant smoke is still primarily driven upward from the porte-cochere and would likely not reach the main building unless strong winds directed the hot gases.
​
​10-foot Separation
Now imagine this same porte-cochere, but this time centered only 10 feet (3 m) from the main building. Radiation heat transfer is now 10 times greater than the 30-foot distance, and 100 times greater than the 100-foot distance.
Picture
At only 10 feet from a 5 MW fire, the heat flux is enough easily cause 2nd degree burns for unprotected skin.

Additionally, this heat flux is now approaching the critical heat flux for ignition of some building materials. The critical heat flux is the minimum amount of heat, per area, required to cause ignition. There's several factors that contribute to ignition including exposure time, material thermal properties, surface temperatures, and the actual heat flux versus critical heat flux - but for our purposes I'm only showing this critical heat flux for a couple siding materials.

Wood, for instance, has been tested to have a critical heat flux of approximately 10 kW/sqm. Vinyl siding has a critical heat flux of approximately 15 kW/sqm (both values from SFPE Handbook of Fire Protection Engineering, Table A.35, 5th Volume).

When we look at the heat flux already produced by a fire of this size at 10 feet we can see that we're already approaching the critical heat flux for both wood and vinyl.


Picture
Actual Separation

Now let's speak in practicality. Porte-cocheres are built to allow visitors to enter and leave cars without exposure to rain or sun. Is a 30-foot or 100-foot separated porte-cochere provide any value to a building? No, of course not. This exercise just shows that with reasonable assumptions, a 10-foot physical separation assuming a 5 MW fire begins to approach the critical flux needed to ignite a nearby building.

Fire Size

Would the actual fire be 5 MW? It's difficult to predict and will vary widely by the materials used and the shape it conforms. A point-source approximation is a large oversimplification given that a wooden canopy would burn in a very different configuration than a condensed pile of wood pallets, for instance.

Convection

What about convection? Up to now we've still only discussed heat transfer by radiation. If a porte-cochere is close enough to a building, convective heat transfer from the hot smoke will begin to contact the main building and heat surfaces along the face of the main building. This could also be aided by wind conditions as well.

As I explored a little last week, a porte-cochere that is only separated inches or a couple feet from a building is hardly any different than a porte-cochere that's attached to the building. That's largely because of convective and radiative heat transfer. The further away the porte-cochere is, the less convective heat transfer plays a role and the lower amount of radiative heat will be transferred.


Fire-Resistive Construction

What if we create a firewall or fire barrier? Both would slow the spread of fire and help prevent the main building from burning. The International Building Code​ relaxes the physical separation with fire-resistive construction, and for good reason. Heat flux becomes much less important when the exterior is of non-combustible construction.

Summary

It can be easy to get lost in code minutiae and live by the black and white lines of what code reads. I find that it's important to remind myself about context about each building and where good engineering judgement plays a role in protecting buildings from fire.

This overly-simplified series of calculations just shows the tiers of radiative heat transfer and how much it is affected by the separation distance. The further away a building is from another, the less convective heat transfer plays a role (if any) and the less radiative heat transfer occurs. 
 
If you found this interesting, let me know by leaving a comment here. Always happy to hear other opinions. If you don't already follow the weekly blog, consider subscribing here. Thanks for reading!

Comments are closed.
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    AI
    Announcements
    Author Jocelyn Sarrantonio PE
    Book Review
    Calculators
    Career
    Course
    Delegated Design
    Design Challenge
    Detail Critique
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Opinion
    Passive Fire Protection
    PE Exam
    Perspective
    Pick A Part
    Pick-A-Part
    Products
    Site Updates
    Special Hazards
    Specifications
    Sprinkler Systems
    Standpipes
    Students
    Talks
    Tools
    Videos


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    January 2025
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT