What is the Best Height for Sprinkler Pipe?

7/19/2017

 
I have heard several times (often from those outside fire protection) that sprinkler pipe should be located "wherever it can fit around everything else," or something to the effect of "the sprinkler contractor will figure it out."

It is under that same mentality that mechanical and electrical engineers will complain when the fire sprinkler contractor is first to installation and they now have to redesign portions of their ductwork or conduit runs.

Is it really the sprinkler contractor's fault if no one allocates space for sprinkler pipe in the first place?

Coordination often comprises the most difficult and commonly the most overlooked part of building systems design. Ideally, where should sprinkler pipe be located above a ceiling?

I've asked a handful of designers, engineers and installers for their take on what the ideal height of sprinkler pipe is to effectively coordinate with other systems while minimizing extra pipe. While each project will vary in detail, much of the consistent thought has been to locate fire sprinkler pipe above the top plane of lay-in lights and underneath ductwork while routing to avoid can lights and slot diffusers (which tend to be deeper than lay-in light fixtures). The lower the sprinkler pipe, the less pipe required to create the drops down to each sprinkler.

In my experience (and as others have concurred), locating the pipe centerline 8-inches above the finished ceiling often works well. Under this location it is still important to avoid routing over the centerline of light fixtures, or over diffuers, deep can lights, and slot diffusers. While LED lights have helped keep the depth of lay-in fixtures to less than older fluorescents, it is still important to avoid the centerline of lights as to avoid the fixture hangers. Greater depths or conflicts with any of these elements can of course raise the centerline up to 10 or 12-inches above the finished ceiling.
Sprinkler Pipe Coordination
That being said, the ideal height of sprinkler pipe can be impacted by two other concepts: concealed space protection and seismic bracing. Where concealed spaces need to be protected (such as in combustible construction applications), it may be worthwhile to raise the pipe closer to the underside of the wood structure.

Another important consideration is when seismic bracing is required. Where there is a significant distance between the buildings' structure and the pipe, seismic bracing begins to lengthen and as a result must have greater reinforcement (larger pipe diameters for lower slenderness ratios). In these scenarios, it can be easier to shorten the bracing lengths by raising the system closer to the height of structure.

Regardless of where pipe is to be located, establishing space for sprinkler pipe early in a project is a benefit to both upfront engineers and contractors on the back end. 

What is your routing preference? Have you found any height to be more ideal than others? Feel free to comment if so.

If you've found this helpful, please consider forwarding to others who might be interested. Anyone can subscribe to these weekly posts, for free, here.

Eric P Rogers
7/21/2017 05:53:39 am

The location mentioned doesn't take into account seismic bracing for all the MEP systems above this Ip = 1.5 sprinkler piping. Many don't fully grasp that whether these systems fall under the exception, if they cause damage to the sprinkler pipe in a seismic event, then they must be

David Koopman
7/28/2017 07:53:22 am

Being from a region that does not require seismic bracing, I have to agree with 8" above the ceiling. I try to establish this and 6" off either wall in the corridors. Before BIM coordination began it was no problem, we established zones in the kick off meeting and if you left your zone creating conflicts with other trades it was your respisibility to work them out. Today with BIM and the specs being written in a way that gives the mechaical contractor free reign it's almost easier to not draw anything until everyone else is coordinated. For some reason it's always the sprinkler guy stuck re drawing the system multiple times, most times ending up very close to our original design. I understand coordination is give and take but, in today's industry the expect us to give everything.


Comments are closed.
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    AI
    Announcements
    Author Jocelyn Sarrantonio PE
    Book Review
    Calculators
    Career
    Course
    Delegated Design
    Design Challenge
    Detail Critique
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Opinion
    Passive Fire Protection
    PE Exam
    Perspective
    Pick A Part
    Pick-A-Part
    Products
    Site Updates
    Special Hazards
    Specifications
    Sprinkler Systems
    Standpipes
    Students
    Talks
    Tools
    Videos


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    January 2025
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT