New Occupant Load Factors Coming to NFPA 101

11/29/2017

 
Not all code revisions are more conservative.

The 2018 Edition of NFPA 101 has updated the long-held occupant load factor of 100 sqft per person to 150 sqft per person. If you don’t live in the life safety arena, this change allows the calculated occupant load for a business space to be notably less, thereby requiring less exit width, stair width, potentially the number of exits, and other means of egress requirements.

Origins
The 1934 Building Exit Code first incorporated the density of 100 sqft per person, which was based upon a 1922 recommendation from the Building Exit code committee. It has since carried through over eight decades of code revisions and has lasted through many differences in office design.

Concentrated Business Use Introduced in 2015
The Life Safety Code introduced the Occupant Load Factor for “Concentrated Business Use” at 50 sqft per person in the 2015 Edition. 

The goal with determining occupant loads has always been to provide the means of egress for a maximum probable number of occupants, and the introduced higher density was intended to address higher-density spaces than would normally be expected in a business occupancy. Annex material in NFPA 101 states that this should be applied where occupant concentrations are maximized, such as business call centers, trading floors, or data processing centers.

Open Office Concept Building Occupant Load
Modern open office concepts have changed the way we congregate and occupy buildings

Challenges with High Occupant Loads
This 2015 Edition change, according to testimony in committee hearings for 2018, has brought increased scrutiny and sometimes higher occupant loads to business occupancies by review authorities. 

Increased occupant loads impact egress capacity, additional exiting, and can be very difficult to achieve higher occupant loads in existing buildings. Without additional horizontal exiting or plumbing fixtures, many existing office buildings cannot accommodate redesigns under higher occupant loads.

Open office concepts have also introduced new challenges. Collaborative spaces are sometimes being reviewed as assembly, even though these small rooms are intended and often used by the same people that are no longer at their workstations. The occupant load could effectively double-count the same occupant for two different work areas.

​While terminology for the collaboration rooms is not entirely defined, modern office buildings are often labeling these as huddle rooms, quiet rooms, focus rooms, enclave rooms, or other owner-specific terms. These type spaces appear to meet the intent for the new collaborative room load factors identified below.

Collaboration Room, Business Occupant Load Factor
Collaboration rooms, often labeled as huddle, quiet, focus, or enclave rooms, are often used for smaller group activities by people who otherwise occupy the open office space. These smaller spaces function differently than traditional conference rooms.

Researching New Load Factors

The NFPA Fire Protection Research Foundation sought to study the appropriateness of the business occupant load factor for modern buildings in 2012. 

Two studies stemmed from their initiative; a WPI Student Research project studies office building designs, modern changes in the workplace, and occupancy impacts of flexible employee scheduling and telecommuting. This study suggested it would be reasonable to increase the load factor to 150 sqft per person. 

The second study, by Gilbert Group at the University of Canterbury in Spain, found average load factors for modern office buildings averaged 181 sqft per person. Both studies summarized that the 100 sqft per person occupant load was considered conservative.

Further testimony in the committee hearings suggested that at least ten research studies on office buildings conducted since 1935 have indicated that the Occupant Load Factor for businesses was conservative at 100 sqft per person.

Resulting Changes
The research, motions, and resulting voting brought a few major changes to the 2018 Edition of NFPA 101. Business use occupant load factor has increased from 100 sqft to 150 sqft per person; the “Concentrated Business Use” load factor has remained from the 2015 edition; and lastly small collaboration rooms and large collaboration rooms (with a threshold at 450 sqft) are given occupant load factors of 30 sqft and 15 sqft per person, respectively:
NFPA 101 Business Occupant Load Factor
NFPA 101 Updates to Business Occupancies by Year

Relevant Notes
While the discussion above considers the process for NFPA 101 Changes, the International Building Code has similar provisions for the 2018 Edition for Business Occupant Load Factors as well as definitions of net and gross floor areas (Table 1004.1.2 and Chapter 2 Definitions, respectively).

Lastly, occupant loads of 50 people or more in a single space would still consider the space to be assembly and not a business occupancy. Large presentation rooms, training areas, or lecture halls can quickly introduce assembly occupancy requirements that are unaffected by these changes.

Subscribe
Find this article helpful? Subscribe for free or forward to a friend.
Janet A Washburn
12/3/2017 05:59:02 pm

Very useful article, thank-you!

Kevin Sneed
9/6/2018 09:34:48 am

It would be better to see the comparison between 2015 IBC & 2018 NFPA 101 regarding occupancy loads.

Shannon
1/8/2019 10:49:06 am

I believe the business occupancies use the gross floor area, per note "a" on Table 7.3.1.2

Tony Tso
6/16/2019 09:34:01 pm

Exactly. So I would love to see the author's basis for stating that NFPA 101's "new occupant load factors use the more modern net square footage...instead of gross square footage."


Comments are closed.
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    Announcements
    Author Jocelyn Sarrantonio PE
    Book Review
    Calculators
    Career
    Course
    Delegated Design
    Design Challenge
    Detail Critique
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Passive Fire Protection
    PE Exam
    Perspective
    Pick A Part
    Pick-A-Part
    Products
    Site Updates
    Special Hazards
    Specifications
    Sprinkler Systems
    Standpipes
    Tools
    Videos


    ARCHIVES

    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    January 2025
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE 100-Day Marathon
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT