MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

How Precise Is Your Flow Measurement?

3/19/2024

 
​When you conduct a hydrant flow test, how precise is your resulting measurement?
 
Let’s say a flow test summary shows 82 psi static, 54 psi residual at 956 gpm.
 
Is it really 956 gpm? 
Picture
Well, no, of course – but 956 is the best resulting estimate of the flow test with the information and measurements we have at hand. It’s where the dial best predicts.
 
But how precise is that measurement, really?
 
Are we certain that it’s 956 gpm and not 957 gpm, or 960 gpm, or 1,000 gpm?
 
Now of course, a hydrant flow test is a point-in-time measurement. It’s not representative of daily fluctuation or seasonal fluctuation.
 
Let’s save that discussion for another time. What I’m really interested in is when we take a flow test or run a pump test, how accurate are our results, really?
 
SIGNIFICANT DIGITS
The concept of significant digits is one simple way avoid suggesting a higher level of precision than a measurement justifies.
 
In other words, if our flow test results said 956.21 gpm, we’re suggesting, based on the decimal placement that we actually know that the value is not 956.4 gpm; it’s instead between 956.2 and 956.3. That’s a level of precision that is suggested by significant digits.
 
Technically, if we had a pitot gauge reading of 9 psi during a flow test, then we would have one significant digit.
 
Using one significant digit is very problematic in flow test results.
Q=29.84×C×d²×√P

In this flow conversion formula above (the Freeman Flow Formula), we take we take pitot pressure (P), opening diameter (d), and the Coefficient of Discharge (C), to get a resulting estimate of flow through an opening.
 
The problem with using the significant concept is that a pitot reading of a single digit value would mean that we round our resulting flow would yield one significant digit.
 
LOW PITOT MEASUREMENT
NFPA 291 actually recommends that pitot readings less than 10 psi should be avoided, if possible. That would mean flowing fewer outlets to get a higher pitot reading to avoid inaccurate readings.
 
So, at least in theory, three 2.5” outlets with a C-factor of 0.90 and a pitot of 9 psi each would result in a flow estimate of 1,511 gpm being rounded to – what – 1,000 gpm or 2,000 gpm?
 
The concept of ‘significant digits’ here would result in massive rounding error.
 
This line of logic is where I was really curious about our flow test results – or really any measurement of flow, such as pump testing.
 
How precise are our measurements?
 
BIG GAUGES, SMALL TICKMARKS
If you’ve tried to take a close reading and nitpick the difference between 96 and 97 psi on a 300 psi gauge – that can be extremely difficult to do. Yet, at least in the case of fire pump testing, that result can be the difference between passing or failing a fire pump test.
Picture
How precise can we read a higher-range gauge with small or grouped tickmarks and a small-diameter face?
​If you don’t think that’s a high-stakes proposition, then I’d invite you to wrap up final acceptance testing on a federal project with every stakeholder present and watching. It can be high stakes.
 
Perhaps the more appropriate way to understand precision is by doing error propagation on this conversion.
 
Error propagation is a sore point for me, as I pretty much failed every physics lab in college that required it. Time to shed those demons.
 
If you’re not into math, skip ahead to the summary to see where I ended up.
 
I want to show my work here as I haven’t seen this done and I’m very much for transparency and getting feedback, especially when I venture a little beyond my own fenceposts.
 
ERROR PROPAGATION FOR FLOW TEST CONVERSION
Error propagation is a fancy way to describe the reliability of the resulting calculation.
 
How precise is the result?
 
That’s what we want to know – and knowing so can help us make more informed decisions in our assessments. 
Picture
A formula with multiple variables, where each have their own uncertainty, the overall uncertainty depends upon how each variable affects the final result.
 
In other words – if I’m not exactly sure about the numbers I’m putting in, how unsure should I be about the answer I get out?
 
IMPACT OF DIAMETER VS. PITOT PRESSURE
In this equation, a percentage error in measurement of a diameter could have an outsized effect on the resulting flow since diameter is squared.
 
To run an error propagation on a formula involving variables which are multiplied together, we square the relative uncertainty (change in a measurement divided by the measurement), square them, add them together, and square out the result. 
Picture
​EXAMPLE: 60 PSI GAUGE
So, let’s say we ran a flow test where we were certain in the Coefficient of Discharge (0.90), we measured and were confident in the diameter of 2.5 inches (within a 1/16th of an inch), and took a pitot reading of two side outlets each at 8 psi using a 60 psi gauge with 1% accuracy.
​
Practically speaking, that’s a very reasonable amount of tolerance of a normal hydrant flow test or fire pump test.
​
With those results, we would calculate a total flow estimate of about 950 gpm. 
Picture
​How precise is that flow?
Picture
(Error in flow test reading measuring opening within 1/16” and pitot with 60 psi gauge)
​
So, with a variation of + 59 gpm, our resulting flow estimate would be 950 gpm + 59 gpm, or a resulting range of between 890 gpm and 1010 gpm.  
 
That’s a pretty wide variation – and it’s certainly a lot wider than I would have expected considering we’re using a 60 psi gauge with 1% accuracy.
 
EXAMPLE: 100 PSI GAUGE
What would happen if we used a 100 psi gauge with 1% accuracy?
Picture
(Error in flow test reading measuring opening within 1/16” and pitot with 100 psi gauge)
​
​EXAMPLE: 300 PSI GAUGE
Taken to an extreme – what if we used a 300 psi gauge to measure pitot? A bad idea for sure (it’s nearly impossible to read sensitive low amounts, and likely in the least-accurate portion of the gauge. But just for kicks:
Picture
(Error in flow test reading measuring opening within 1/16” and pitot with 300 psi gauge -
​which we would never recommend doing)

​EXAMPLE: 60 PSI GAUGE WITH IMPRECISE DIAMETER
Now, what if we were less confident in the actual inside diameter of the hydrant side outlet? What if we thought it was 2.5”, but only within an 1/8th of an inch? With our 60 psi gauge:
Picture
(Error in flow test reading measuring opening within 1/8” and pitot with 60 psi gauge)
​
Yikes! Did you notice that?
 
Even with a 60 psi gauge, if we only know the inside diameter within an 1/8th of an inch, it’s worse than using a 100 psi gauge.
 
Knowing the precise inside diameter is important as it has a huge effect on the level of precision.
 
HOW DO WE IMPROVE PRECISION?
Based on the inputs – there are a few key ways to improve the precision of flow test readings when we use pitot gauges to estimate the amount of flow.

I’m interested in writing more on this in the coming weeks, but there are a number of ways in which we can improve the precision of our flow testing and have more confidence in our results.
 
#1 MEASURE THE OPENING SIZE
First – and probably the most important based on our calculation – is to know the exact diameter of the orifice opening.
If we are flowing out the side of an outlet, we actually need to measure, with precision, the inside diameter of that opening. As I’ve been told, not all inside diameters are equal. They depend on the exact make and model of a hydrant.

I’ve made this mistake before and assumed all 2.5” side outlets are the same inside diameter.

To improve precision, take a careful measurement of the exact inside diameter of the opening down to the 1/16th of an inch.

Alternatively, using a factory-created attachment with a factory-milled opening will help define and make that variation go away.

A known diameter with a very tight factory tolerance helps us reduce or eliminate this concern altogether.

#2 USE SMALLER RANGE GAUGES
In general, we want to use the smallest range for the gauge possible.

Using a 300 psi gauge to measure anything within 0-30 psi is problematic. Not only is that a less-accurate range for a gauge (near the ends), it’s extremely difficult to read. The tickmarks just become too small to read well.

Instead, we want to use the lowest gauge range that’s possible for the test.

If we’re expecting results below 100 psi, can we use a 100 psi gauge instead of 200 or 300?

If we’re measuring pitot and expecting values under 60, can we use a 60 psi gauge?

Even a 30 psi gauge?
​
The bigger the tickmarks and the smaller the range, the better we’re going to be able to see and read the results.
Picture
Using a lower-range scale gauge can lead to far-easier reading of the gauge,
​but also be within a more accurate range for the gauge itself.

#3 LARGER-DIAMETER GAUGES
This goes against my “travel with small things” concept, but larger-diameter gauge faces are so much easier to read in the field.

They cost more. They’re bigger. But man are they easier to pull values from.

Again – on an important fire pump closeout with many people all watching – having nice clear results to prove the system works as it should helps.
 
#4 USE CALIBRATED GAUGES
For fire pump testing, NFPA 20 requires that all gauges undergo annual calibration testing and be accurate within 1 percent. (NFPA 20-2022 Section 14.2.6.1.2)

For fire hydrant flow tests, that same mandate doesn’t necessarily apply. NFPA 291 is a recommended practice, and requires calibration within 12 months, but is not necessarily enforceable in the same way that NFPA 20 is.

Now, if you’re on a federal project and NFPA 291’s “shoulds” become “shalls”, then there are enforceable teeth.

But for private practice work, many flow tests are simply run with whatever gauge is on the truck that day.

Using a calibrated gauge will obviously hone in for more precise measurement.
 
#5 USE STREAM-STRAIGHTENERS
NFPA 291 now specifically states a preference for playpipes or stream straighteners to improve the accuracy of readings.

Not only do these address the precise opening sizes we talked about earlier, but they hold the pitot measurements in a fixed-in-place mounting position.

This also means we should be measuring at exactly the right center-of-stream location.

This is explicitly listed now in NFPA 291 (2022) Section 4.6.2.
 
SUMMARY
Doing a little error propagation highlights a few things about the measurement process in a calculated way.

We can look at the accuracy of our input measurements an in turn, get a level of confidence about the resulting range of flow from those measurements.

The more precise we are able to measure, the more confidence we have in the result – which is both an obvious ‘gut-feeling’ but can also be mathematically proven.
 
YOUR TAKE
I’m interested in your take.

What are your tips for more accurate readings?

What stories do you have about fire pump acceptance testing or hydrant flow tests in this regard?
 
NEXT STEPS
I’d like to venture down this rabbit hole just a little further.

My next thought is to apply the error propagation concept into a quick calculator tool where you could see your error range yourself – and experiment with different situations.

You might just find an error range based on your normal test equipment that could present your test results in a more appropriate and transparent way.

That's TBD (to be developed).
 
Thanks for reading – and, as always, for fighting the good fight. Have a great rest of your week.
​
- Joe
Robert Bennett
3/20/2024 12:25:37 pm

Thank you for this explanation. There are several accuracy improvements that we try to incorporate into the flow test. Unlike your example we have a very robust water system that causes some of its own issues. High static pressures 165 to 230 PSI are normal for our system. We require that the volume of water flowed create at least a 10% drop of the static pressure or that the volume flowed must exceed the sprinkler/standpipe/pump demand. We preach that the pitot reading be within the center 1/3 of the gauge and that the gauges be recently calibrated. This has been an ongoing fight with the contractors but by your example when the hydraulic calculations run the supply and discharge numbers out to three decimal places there is no accuracy to the calculation. But the designers think that they are spot on. When they design right up to the supply curve they may not actually have the volume they think they have.


Comments are closed.
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    AI
    Announcements
    Author Jocelyn Sarrantonio PE
    Book Review
    Calculators
    Career
    Course
    Delegated Design
    Design Challenge
    Detail Critique
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Opinion
    Passive Fire Protection
    PE Exam
    Perspective
    Pick A Part
    Pick-A-Part
    Products
    Site Updates
    Special Hazards
    Specifications
    Sprinkler Systems
    Standpipes
    Students
    Talks
    Tools
    Videos


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    January 2025
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT