Are Sprinklers Required in Closets?

6/12/2018

 
Based on the feedback and response about an earlier article about Sprinkler Requirements in Bathrooms, it only makes sense to extend a roadmap for navigating requirements concerning sprinklers in closets.

​For such a simple topic, this work took two weeks and will still require further exploration in the coming weeks.

Basic Concept
The premise for determining whether a closet requires a sprinkler would intuitively be fairly easy, as the question implies a yes/no black and white answer. The development to get to where we are currently, however, is governed by experience and studies into the risk/benefit posed by providing sprinklers in closets.

Does providing a sprinkler within a closet improve building protection and aid in better life safety? Yes, in most (or perhaps even every) circumstance.
​​
Picture
While in concept determining whether a sprinkler is required for a closet would typically be a straight-forward cut-and-dry process, the code path to determine whether it is required or not is dependent upon multiple factors.

Competing Objectives
However, there are also competing objectives for standards such as NFPA 13R (Low-Rise Residential Occupancies) and NFPA 13D (One- and Two-Family Dwellings and Manufactured Homes), which is to create affordable systems with a life-safety objective in lieu of property protection.

Attempting to create affordable systems is not inherently a bad thing; it only creates less friction between the building owner paying for or deciding to install a sprinkler system. 

Why Not All Small Closets?
Why is a 10 sqft apartment closet any different than a 10 sqft closet in a motel? They could be constructed the exact same.

The difference is in the totality of the situation: NFPA 101 and by extension NFPA 13 recognize that "inherent ignition sources and combustible fuel load" are very different for different occupancies. In general, where closets can more easily accumulate high fuel loads (longer-term living situations), the less likely a sprinkler will be allowed to be omitted.

NFPA 101 - what about the IBC?
NFPA 101 outlines specific allowances based upon occupancies to determine closet sprinkler requirements. The International Building Code does not address these same areas, rather deferring those requirements to NFPA 13, 13R, or 13D. 

What if both IBC and NFPA 101 Apply?
Many healthcare applications find that the IBC is enforced by a local jurisdiction while NFPA 101 applies due to healthcare credential requirements of CMS (Centers for Medicare & Medicaid Services). Typically the most stringent requirement would be the guiding direction in these instances, but it would be prudent to work with code authorities to resolve these conflicts where they arise.

2016 Edition Changes
The 2016 Edition of NFPA 101 offered a handful of changes specific to closets. You'll see in the breakout below that this flowchart only applies to the 2016 Editions of NFPA 13, NFPA 13R, NFPA 13D, and NFPA 101. With so many changes between the editions, I'm planning to recreate this chart with prior editions for reference.

The Flowchart
The chart below is a visual summary of the decisions that lead to various sections of code. Despite the simple yes/no nature of whether a sprinkler is required in a closet or not, you'll notice the complexity of the decision tree within NFPA 101. Click on the chart for an enlarged version below.

​
Picture
Flowchart for 2016 closet fire sprinkler requirements

​Don't get these articles already? They're free - subscribe here.
GET PDF CHEATSHEET
Munir Malick
7/3/2018 10:00:14 pm

Very nice for professionals & Technicl Guide

Tom
10/23/2018 12:15:32 pm

Residential closet Massachusetts 24sqft or if the lesser dimension is greater than 3ft is how I understand closet rules.Is this correct or incorrect I'm asking because I have recently been told the 3ft rule is now extinct and it's based solely on sq ft.

Chuck Sullivan
4/23/2019 02:45:44 pm

I need rulings on sprinkler heads in closets or state of Arizona for assisted living

Susan Olson
8/9/2019 12:13:23 pm

My son has purchased a condo, (prior apt conversion). They removed the closet doors in the living room related to an air flow vent return on one side for the central air added. There is a sprinkler head is in the center of the former closet but the sprinkler would be for the full living room. I was told I can not enclose the sprinkler in a closet when I wanted to build the closet doors 3/4 of the way, (leaving 35 inches for the air flow vent). So, now the closet would be only 40" wide. Do you know in MN if I can enclose the sprinkler? Thank you.

Moderator
8/13/2019 08:55:01 pm

Hi Suan,

Your question is posted on the daily forum here: https://www.meyerfire.com/daily/can-sprinkler-be-enclosed-in-small-closet

Please see the link and read the post - there may need to be some clarification for your question. Thanks!

Dave
5/12/2020 03:46:33 pm

When does NFPA 101 take precedence over NFPA 13 in regards to omitting sprinklers in closets less than12 sq ft in area in individual dwelling units of new apartment buildings.

We have a 44 story high rise with 10 sq ft closets 2'x5' and we are trying to eliminate the sprinklers.

NFPA 13 would require them since it is not a hotel or motel but NFPA101 allows for the omission.


Comments are closed.
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    AI
    Announcements
    Author Jocelyn Sarrantonio PE
    Book Review
    Calculators
    Career
    Course
    Delegated Design
    Design Challenge
    Detail Critique
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Opinion
    Passive Fire Protection
    PE Exam
    Perspective
    Pick A Part
    Pick-A-Part
    Products
    Site Updates
    Special Hazards
    Specifications
    Sprinkler Systems
    Standpipes
    Students
    Talks
    Tools
    Videos


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    January 2025
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT