Does anyone have experience with a mamava (mobile lactation room/pod) being placed in a commercial business occupancy?
The square footage is approximately 50 sqft. It is composed of only Class A rated materials (flame spread index). From a practical perspective it does not make sense to me to drop a sprinkler in. However, I'm hard-pressed finding an exemption from code (NFPA 13 or 101) to not sprinkler the space since it's inhabitable and not a bathroom or closet (which I know they are exceptions for sprinklering based on size). Posted anonymously by a member for discussion. Discuss this | Submit a Question | Subscribe
11 Comments
Kelly
4/11/2019 10:20:18 am
I would be interested to see what others think about this too. I have seen these in airports and convention centers but have not had to deal with it in a design yet.
Reply
Don Pierce
4/11/2019 11:10:22 am
The NFPA Journal published an article in September of 2018 that provided guidance for how I treat all "privacy pods." The title, "Navigating the sprinkler requirements for office pods," by Brian O'Conner.
Reply
JOE
4/11/2019 11:19:28 am
Here's a link to that article: https://www.nfpa.org/News-and-Research/Publications-and-media/NFPA-Journal/2018/September-October-2018/In-Compliance/NFPA-13
Reply
Maggie
4/11/2019 11:52:21 am
I think, since it is not fixed, then it should be treated like a movable object therefore no sprinkler head.
Reply
Sean
4/11/2019 12:25:44 pm
Don't assume it's movable. The question does say room.
Reply
Sue
4/11/2019 12:55:28 pm
The building code requires anything that weights more than 400 lbs to be anchored. It also requires anything over 5'9" be secured from seismic movement. So we (at least in earthquake country) would put a fire sprinkler in because it is now a fixed room.
Reply
Sean
4/11/2019 12:27:39 pm
Bathrooms are only exempt within some dwelling units. If they build out a room for it I would require a fire sprinkler head inside it.
Reply
WES
4/11/2019 12:33:26 pm
It seems as though the potentially portable/moveable feature could make it similar to furniture and the limited-combustible nature of the outside helps.
Reply
Evan
4/11/2019 12:39:54 pm
This intrigued me so I went and looked at one of these units at the airport today. It looks like the only services connected to the unit is a single 120v circuit. This powers 6 can lights, a quad power receptacle, and a small exhaust fan. No fire protection and no fire alarm. Inside the unit the 'ceiling' is partially open to the area above. There is an approximate 2'x6' grid that exposes the interior to the ceiling above. My thought is that possibly because of the size of the solid ceiling compared to the grid ceiling it could be viewed as less than 48" in width and therefore is not an obstruction to sprinkler flow?
Reply
Sue
4/11/2019 12:44:28 pm
As the AHJ our ordinance requires all "rooms" in a fully sprinklered building to have a fire sprinkler in it. We have them in small walk in freezers and refrigerators. We have modified our requirements to include bathrooms, closets, etc to have fire sprinklers.
Reply
Dean Melanson
4/12/2019 12:09:33 pm
Since it is in a commercial occupancy, occupied, not furniture, and if it has a ceiling that would obstruct sprinkler spray into the space it would be required by code to be protected.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |