Does NFPA 13 limit the friction loss per foot of pipe? What is good practice to follow in calculation process?
Posted anonymously by a member for discussion. Discuss this | Subscribe
13 Comments
John P Malescio
2/20/2019 10:08:32 am
NFPA-13 does not have any restrictions on piping velocities, but NFPA-20 does have restrictions.
Reply
Anon
2/20/2019 10:47:10 am
There are no velocity limits in NFPA 13.
James
2/20/2019 10:30:17 am
While accurate, this is a baseless response. There is no maximum requirement in NFPA 13 or in building codes for hydraulic calculations. However, NFPA handbooks tell you to use velocities between 10-20 ft/s. The reason is that the values of the friction loss coefficients used are accurate only if the flow velocity is close to that at which the value of C was measured.
Reply
James
2/20/2019 10:32:46 am
To be specific, this is for the hazen-williams equation.
Anon
2/20/2019 10:51:06 am
John, that is consistent with what I have read.
PETE
2/20/2019 10:44:55 am
I set a warning threshold at 32 fps in hydracalc, and don't really even pay attention to that if it is only in the node segment supplying the most hydraulically remote sprinkler (nearest sprinkler on the furthest line). Velocity pressure only accounts for a small percentage of the total pressure, and any deviation from the Hazen-Williams formula can be correct for with all of the other safety factors in the NFPA 13 standard. Velocity pressures DO need to be accounted for in other types of systems, but if you're concerned about it, AutoSprink calculations automatically include the velocity pressure in the calcs.
Reply
Franck Orset
2/20/2019 11:02:37 am
No restriction from NFPA
Reply
Franck Orset
2/20/2019 11:09:22 am
I suddenly realized, by reading again the question, that the answer is not to the question (as well as all the answer above).
Reply
Anon
2/20/2019 12:02:16 pm
[sheepishly] I also did not read the original post correctly, and went straight down the old velocity rabbit hole. I concur with Mr. Orset.
Patrick Drumm
2/21/2019 07:15:16 am
I agree that there is no requirement regarding limits of pressure loss per foot in NFPA #13. It can be important to keep in mind high pipe velocities and high pressure loss when designing systems, because if changes are needed to be made in the field in these areass due to any number of issues (coordination, lighting location changes), additional pipe and fittings in these areas can cause signifigant increases in pressure requirments due to the pressure loss per foot previously identified and the added equivalent lenght of pipe you would be adding.
Piero Piemonte
2/21/2019 01:45:02 am
European norm UN EN12845:2015 indicates maximum velocity and not the limit of friction losses.
Reply
In NFPA 13 Ed.2019 include a new statement in the section 27.2.1.4 says : the velocity of water flow shall not be limited when hydraulic calculations are performed using the Hazen - Williams.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |