Is there a maximum height that's permitted between the main roof and a suspended ceiling in order to still omit sprinklers above the ceiling?
Posted anonymously by a member for discussion. Discuss this | Subscribe
6 Comments
Wayne Ammons
2/13/2019 07:52:33 am
If I am understanding your question correctly, you are describing a concealed space above a suspended ceiling. The omission of sprinklers will depend on there being access to the space and the amount of combustibles within the space (also considering construction type). If there is limited or no access and minimal combustibles are present, sprinklers can be omitted regardless of the distance between the suspended ceiling and main roof deck.
Reply
MIGUEL ANGEL D ADARIO
2/13/2019 04:03:56 pm
Dear Wayne
Reply
Wayne Ammons
2/14/2019 07:37:35 am
Unfortunately, there are a number of exceptions of varying scenarios where sprinklers may be omitted. I have copied the section from NFPA 13, 2019 edition concerning concealed spaces below. Hopefully one of these exceptions explain your particular situation:
Wayne Ammons
2/14/2019 07:55:41 am
I realized I copied sections from the entirely wrong edition. Please disregard my previous response and I will follow-up shortly.
Wayne Ammons
2/14/2019 08:29:08 am
Below is from the 2016 edition of NFPA 13, I am having trouble pulling from the 2019 edition:
Franck Orset
2/19/2019 11:15:57 am
Dear Wayne
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |