Where can I find information on how much flow each type of fire department connection can handle (siamese, 4" Storz, or 5" Storz)? Is this provided in a standard, or manufacturers data?
Also, does just about every fire department have the ability to connect to Storz? I've heard from many departments that the FDC type depends on the flow of the building, which leads me to believe that many departments can connect to any type of FDC. Posted anonymously by a member for discussion. Discuss this | Submit a Question | Subscribe
4 Comments
Scott
4/5/2019 11:05:32 am
NFPA did a study through Exponent on the flow capacities of various FDCs (although I don't think Storz connections were tested). See: https://www.nfpa.org/-/media/Files/News-and-Research/Fire-statistics-and-reports/Suppression/RFFireDepartmentConnectionInletFlowAssessment.ashx?la=en
Reply
Robert Bennett
5/20/2021 09:26:32 am
In reading the report it leads you to believe that single FDC is more hydraulically efficient. However a MAJOR shortcoming of the study was they did not include the loss in the supply hose. By example a single 2.5 inch hose flowing 500 GPM has a friction loss of 50 PSI/100ft. When the total system pressure demand is 150 PSI or higher the required pump pressure could reach 225 PSI very easily. This is the practical limits of the hose, so although single FDC is definitely more efficient the whole system must be considered when designing systems.
Reply
Richard Mercer
4/5/2019 12:01:48 pm
It's not the fittings by themselves s that determine the flow capacity of the FDC piping arrangement, the size and arrangement of the piping to the system, determines the flow capabilities. The friction loss of the LD Storz connections is minimal. (4 or 5" Storz x 4" PT)
Reply
Dean Melanson
4/5/2019 12:38:55 pm
An additional issue with the number and size of the inlets lies with the local FD responding and the location of the nearest hydrant.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |