What range of heights are allowed for standpipe hose connections above the landing in a stairwell?
Any advice as to arranging the hose connection (height, orientation, etc.)? Posted anonymously by a member for discussion. Discuss this | Submit a Question | Subscribe
4 Comments
Wayne Ammons
2/25/2019 08:18:55 am
From NFPA 14, 2016 edition:
Reply
Nimal Tissa Wijetunga
2/25/2019 11:40:27 pm
900 mm to 1200 mm from the floor level
Reply
David Cross
2/26/2019 10:25:15 am
There are also local AHJ requirements that should be vetted as well, some AHJ's want it at a specific elevation or have specific clearances when installed in a cabinet etc...
Reply
Franck
3/4/2019 11:41:38 am
In all cases, be just practical.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |