If there’s one big hairy problem in the fire protection industry that everyone knows about, yet few take head-on, it’s the delegated design problem. The practice of delegating pieces of the fire protection design has been around forever. THE CURRENT REALITY Some harsh but perhaps true realities today as an industry:
Out of those realities has been “delegated design”, where a professional engineer stipulates (specifies) what they deem critical, and “leave” the details to the installing contractor. GOOD VS. BAD If done well, delegated design can:
If done poorly, delegated design can:
THE CENTRAL ISSUE At the risk of sounding highly dramatic, I see this as the central issue that plagues our industry in North America. It is awful. And if you haven’t seen it, then ask your local estimator. What do they see? Is the scope of work well-defined? Or are they seeing documents that are simply full of landmines? Where a quick note on plumbing plans or buried in a specification could mean tens of thousands of dollars of cost that the contractor is supposed to eat? A DISSERVICE We, as an industry, do a terrible disservice to everyone else in the way that we do delegated design. Terrible. This isn’t a regional issue, either. I didn’t know it was this bad until I started working for contractors and I saw what they saw. And good grief, it’s terrible. SO FULL-DESIGN? Now conversations about this usually then go to – fine – what would you have Joe? Full design, every time? What about a single-family home? We don’t have enough FPEs for complex projects, much less residential sprinkler design? And I’m with you there – I think the answer is more about reform than it is abolishment. If we simply do delegated design well, I don’t think we’d have the issues we’re seeing today. WHO'S TO BLAME? And, if I’m going to make gross generalizations; if you’re the kind of person who cares about the fire protection industry, or maybe you see your role as being “in” the fire protection industry (like this concept) … then you’re likely not the problem. I tend to find it’s not the people that are concerned about this being the biggest violators. It’s those who don’t care, don’t show up, don’t invest in fire protection. They just “also do” fire protection. That said, the issue needs fixing. CREATING CHANGE Two weeks ago I wrote about working towards change. If 2033 looks different, what is the reality we want to create by then? I think this problem is solvable, and it’s worth solving. A CARROT OR A STICK? Generally, we see fixing incentives as a carrot or a stick problem. Do we use the carrot, or the stick? The carrot entices, rewards, promotes and builds up those that are doing things well. We find ways as an industry to recognize and promote people who do it well. The stick simply beats the violators. It pushes-down, disciplines, penalizes. This might be reporting to state boards or reporting to certification bodies. Right now, we collectively don’t have much of a carrot or a stick.
NO REWARDS? NO PUNISHMENT? We don’t recognize who is doing it well, and we certainly don’t promote them. Heck – we really don’t even have a scorecard or a standard to even identify what “doing it well” looks like! And state boards? What if the people on the board are doing the same bad practices as the violators? Reporting someone to a state board is time-intensive, has little reward, and makes enemies. No wonder so few people go about trying it. And besides that – what do we even compare negligence against? What is our standard practice? If negligence is so widespread, then what really is our standard of care? So, the question becomes, how can we uplift the practice of engineering in our industry when we don’t clearly establish what it is that we should be doing? And even where we have established what that practice looks like – how many of those practicing in fire protection have read and understood it? How accessible is that guidance? WHAT'S THE ANSWER? These are questions and challenges I think we’re up for tackling. I think it can be done. As with all the other impact projects we look at – what is the fundamental answer?
I don’t know the answer, but I think it is within reach. Maybe it’s one or all these things. While some of the writing lately may sound grandiose (and it is my writing, thank you very much ChatGPT), we’re taking active measures to attack this core issue head-on. In the coming pieces over the next few months, I’ll talk about the issue from my vantagepoint, build and ask, and try to open up the dialogue on what a better engineering practice looks like. This is something we can affect, and something I hope you also want to see improved as well. Got ideas on this topic? Share them below. I'd love to hear your input. We can get this right. Thanks for being a part of our community – and as always – as an advocate for what we all do. - Joe
Food for Thought
11/8/2023 11:13:07 am
This is a great post besides not mentioning anything about NICET Certifications and/or NFPA certifications. Many states are addressing this by allowing engineering technicians to work on projects without FPEs if they achieve specific levels of certification (often NICET III or IV or equivalent like NFPA CWBSP). Some states also have supplemental exams. This method obviously has limitations as work becomes more complex, however since there are only a handful of schools with Fire Protection Engineering programs the NICET Certifications and/or NFPA certifications are much better for the industry then having no one qualified at all.
Joe Meyer
11/8/2023 11:27:21 am
This is great, thank you!
Mark Sornsin
11/17/2023 09:38:19 am
The part of the position statement that notes "some jurisdictions have enacted regulations that allow the Technician to layout the system...." has always rubbed me wrong. In my experience the jurisdictions have not actively decided that technicians can design sprinkler systems. Its is just always been that way. I don't believe most state boards acknowledge the degree of actual engineering done by the low-bid contractors. I suspect that they believe the PE working for the A/E team is providing oversight. And when its a design-build project without participation of a specifying engineer... well, that doesn't seem to count as engineering in their minds - or they simply haven't considered those situations.
James Art, FPE
11/8/2023 11:30:14 am
Why the FPE should do a detailed design.
DE
11/8/2023 12:12:13 pm
My take from the contractor's side..
Joe Meyer
11/8/2023 12:25:26 pm
This is great - and I agree on the "just per NFPA 13" part. Those kinds of documents more or less just stay out of the way.
Joe Meyer
11/8/2023 12:27:22 pm
It's probably also worth noting (in my opinion) -
DE
11/8/2023 12:51:49 pm
I misunderstood the "full" design as meaning shop drawings.
James Art, FPE
11/9/2023 12:42:20 pm
But the Engineer needs to know what he is doing!
Mark Sornsin
11/17/2023 09:44:13 am
My experience from my contracting days was that we LOST many jobs because there was no guidance given my the "specifying engineer". We would see a situation that we knew required a higher density but could easily be ignored by other contractors and completely missed by the AHJs. After getting my PE, I found it especially difficult to bid projects because too often I would have to ignore best engineering practices and ethics if we wanted to get the work (no I didn't do that, and we lost those jobs - I long ago got out of contracting).
Dave
11/8/2023 01:02:24 pm
Joe, as you know I’ve been on both the contracting side and the engineering side. The Good vs. Bad you lay out at the start of the article is spot on. But I do my job fully and correctly when I’m on the engineering side (and I do sometimes miss things) I have laid the groundwork with a set of drawings and specifications (criteria documents), for bidding on a level playing field and have protected my client and end-user. Then the sprinkler contractor can do what THEY do best in their deferred design. At the risk of insulting my engineer colleagues (which I hope to join), generally-speaking, my designer colleagues on the contracting side can design circles around most “professional engineers.” (With many exceptions of course.) Being a good designer (and estimator) involves knowing the strengths and weaknesses of your company and those of the competition. I prefer to leave it up to the individual contractor to use their creativity and individual strengths in estimating, design, coordination, purchasing, fabrication, etc. Not locking them into a specific design, except for example, where the architect requests specific routing. On the contracting side, for one of the big-box places where you have to go by their provided design, we were only able to gain an advantage with some out-of-the box (so to speak) fabrication and installation innovations. Except on the smallest of jobs, I fight for specific fire protection sheets over notes on mechanical or plumbing where it might get overlooked. But I can’t do a good job on the engineering side and still have the time to do a good fully-coordinated detailed design. (And in my primary market, while we often do full MEP design, our clients do not pay us for that for fire.) So in my view, full design is not the answer, but as an industry we do need to work amongst ourselves and with our AHJ’s to promote and enforce integrity and quality design. One of our industry colleagues has been posting on LinekdIn some examples of egregious sprinkler design. This is the battle we face.
Joe Meyer
11/8/2023 01:33:45 pm
Love this Dave! Very well said.
Carson
11/8/2023 10:05:21 pm
Joe, thanks for the article, and Dave very well said! This is something I been saying since I started working for an ASMEP firm. Strangely, less than a week ago I was complaining about this exact issue after performing a third party FP review of a delegated design for a client. Incorrect hazard classifications, no Class 1 standpipe system when it was required, no flow test, high possibility for the need of a fire pump, failed to see the need for a dry system for exterior loading areas, etc etc. I had to bleed all over it and it was signed and sealed by an Mechanical Engineer as a delegated design. It was utterly useless.
Trent
11/8/2023 03:23:05 pm
We've recently been encouraging our architectural clients to allow us to provide full designs on some projects where coordination among the different trades will be particularly important. The entire design team generally works in Revit, so I think this method drastically improves the coordination aspect. However, we've had mixed reviews on this depending on which contractor is awarded the project. One common issue is that the contractors want us to provide material lists. As an engineering firm, we're not interested in being that closely involved with material ordering. I understand why this is a common question though since some of the contractors design and list in AutoSPRINK, and listing from our Revit model or hand listing from the drawings adds an extra step. Another common issue is that we occasionally become heavily involved in the clash detection with the contractors. The MEP drawings provided by our firm are working drawings, but not shop drawings. Even though we've done a decent job of clash resolution internally, the M&P contractors occasionally develop their own models which lead to more clashes with the fire sprinkler system. Since the fire sprinkler contractor is using the shop drawings we produced, they didn't include an additional service to handle this BIM coordination so it inevitably falls on us.
Dave
11/8/2023 05:29:11 pm
Thanks for that similar perspective, Trent. I at least try to make sure by coordinating with the rest of our design team (who are mostly in REVIT now) that there are physical pathways for sprinkler pipe routing, hanging, and bracing, beam pen's when needed, power for my compressors, etc. On most of the types of projects we do, with the funding they have, more design would fall under "additional services" that some clients take advantage of, but most not. I’m on a couple projects now where we are modeling the mains only in REVIT for coordination and clearance purposes. I am fortunate (spoiled?) that most of the sprinkler contractors I get on local my projects are super competent and good to work with.
Mark Sornsin
11/17/2023 09:57:09 am
When we have done "full designs" we generally clarify that we are providing 75% to 95% design drawings. I.e. we will coordinate as much as possible and note that we stand by the pipe sizing, but final coordination is up to the contractor. This is far more than contractors normally get, and greatly reduces the unknowns for bidding contractors, making the bid far more competitive. To be clear, this level of design is rarely purchased by the clients because it costs more up-front. And if I'm being hired by an architect, they've usually already negotiated fees and normally don't want to go back to the owner for me - so they fall back on more delegated design.
Dan Wilder
11/8/2023 06:29:16 pm
The FPE's role for should be to provide the objectives & design criteria only as detailed in 4.2.1 Engineering Documents of the SFPE/NSPE/NICET/ASCET/NCEES Joint Position Statement. This information is easily attainable at the design stage, clear for all parties for a baseline for bidding, and should not be a point of issue unless there is a base change which would warrant a change order anyway. It provides the guidelines for an installing contractor but leaves the means and methods to the people that deal with it daily. If the info isn't available, the provisions for all the other building factors (egress, wall ratings, structural fire protection, HVAC, site water supply) would also all be affected.
Eric R
11/9/2023 01:28:05 pm
Dan,
MarcBielicki
11/9/2023 06:52:33 pm
I believe a good start would be to offer more fire sprinkler courses in school. That way more engineers come out of college knowing the industry than being introduced into down the line. I would also say that to become an FPE you have to spend time in contacting to see what is actually going on. Anyone can copy and paste details, figure out hazards and spec whatever. But can they actually apply it to real world building!? Most of the time no. I couldn’t tell you how many times I’ve had to explain my design to the engineer approving it. I’m also a fan of the engineers NOT suppling full design - this helps weed out the contractors that don’t have designers on staff or know nothing more than how to install. Yes there are many out there. I’d almost like to see a hybrid of contractors with an FPE on staff to assist with projects with the owner and architects from the start of planning. So the project will go from planning, engineering to install all with one team through the life of the project. I’m currently NICET III in design and am working on my FPE to start this hybrid system I feel will be most beneficial, as I work in contracting and don’t ever plan on getting out. I love this industry and really feel my spot is making sure all aspects of a project are done properly and beneficial to all involved, not just does it meet code that I feel the FPEs only care about. That’s my two cents of being in both engineering and contracting.
Renardy
11/10/2023 05:45:00 am
Hi Joe,
Mark Sornsin
11/17/2023 10:22:04 am
Regarding the Carrot or the Stick:
Patrick Drumm
11/24/2023 11:40:55 am
Joe, this was such a great post. I'm disappointed I was just able to read it, and not fully participate in the discussions earlier. Our industry really is suffering from lack of new participation from top to bottom. So many contractors are having trouble finding field personnel and you mention FPE's being too busy because there are only so many of them licensed out there. As you describe there are typically two options to solve a problem (carrot or the stick). In this case, I wonder if a carrot option could work.
Mark Sornsin
11/30/2023 10:54:00 am
Patrick, I thing that's a perfectly reasonable approach. Fact is, many jurisdictions do not require FPEs per se to specify or design fire sprinkler work. If the MEs in those areas, along with any FPEs that are understaffed, were to employ such designers, there would be a significant improvement from the status quo.
Joe Meyer
11/30/2023 01:54:42 pm
Patrick - this is a great idea. One of the hurdles we need to get over in cleaning up the engineering effort is educating and advocating that there are people out there who can help.
Fritz Descovich
12/22/2023 07:02:49 am
I saw this discussion when it first came out 11-09-2023 and wanted to offer some thoughts and opinions. So I subsequently reviewed the related discussion FP Engineering Documents: What Goes In? dated 11/15/2023. And I reviewed the older discussion We Need YOU in Fire Protection dated 06/15/2021 as the subject of a recent email notice dated Nov 18, 2023. At the same time I re-read the NFSA TechNotes dated 10/24/2023 Technical Careers in the Fire Sprinkler Industry. I started to write a reply to this discussion The Delegated Design Problem four times and each time the reply became a lengthy narrative. I finally realized the reply should be as concise as possible but focus on the big picture and not go into a lot of detail. That could turn out to be a college thesis. But I felt some context regarding my history in our industry might be helpful regrading this discussion.
Fritz Descovich
12/22/2023 07:07:50 am
(just to complete my original reply) Comments are closed.
|