Until I did some research recently, I hadn’t realized that NFPA 72 breaks out different definitions for Unwanted Alarms by fire alarm systems. In a way, as an FPE I always kind of shuttered and turned a blind eye to the reality of how much of the rest of the world views fire alarm systems – as a nuisance. Imagine yourself flipping through a book that you’ve pulled off the shelf at the library. It’s quiet; the librarian shushers are about and keeping the noise down. Then suddenly the fire alarm system activates – it’s loud, startling, What is the first thing that comes to mind when this happens? As a fire person, I jump into detective investigator mode. I understand what kind of inputs would trigger an alarm, so I’m naturally very curious on what might have happened. But what about the ‘Average Joe?’ If it’s a calm library on a quiet afternoon, are they in a rush to leave? Or is their first thought “it’s probably a false alarm?” I can tell you by experience that unless there is another signal, like the smell of smoke, sight of smoke, or others moving quickly – most will pay attention and mostly ignore the alarm. They assume it’s a false alarm until they have evidence that suggests otherwise. FALSE ALARMS DON'T REFLECT WELL This is really bad for our industry. The prevalence of false (unwanted) alarms makes people apathetic to the alarm in the first place, and it reflects poorly on us. Is the reduction of false alarms more important than detecting an actual fire event? Of course not. We need these systems to detect and alert us that something is up. But as a downstream effect or a lesser-priority, we also should pay attention to finding ways to reduce unwanted alarms. We want our systems to be trusted and we want people to react when they someday do activate. WE JUST TALKING IT&M? Much can be said about regular inspection, testing, and maintenance of the system. Old and dirty smoke detectors can certainly cause alarm when there isn’t a hazardous condition. But from the very beginning, we can help prevent unwanted alarms by design. That’s something that designers, engineers, plan reviewers and inspectors can help prevent from the very beginning. BRAINSTORMING IDEAS I don’t have all the answers here, but I would like to start the dialogue and open discussion on clever ideas that help reduce unwanted alarm. NFPA 72 has a list of terms that fall under Unwanted Alarm, which is any alarm that is not the result of a potentially hazardous condition. It lists Malicious Alarm (person acting will ill-intent), Nuisance Alarm (alarm by a non-hazardous condition), Unintentional Alarm (person triggers but by accident), and Unknown (no known cause). My gut says that Malicious and Nuisance are the most preventable. How can we discourage someone from activating an alarm as a prank (Malicious), and how can we reduce Nuisance Alarms where there is no actual threat? Here is my shortlist – I am very interested in your tips and takes on additional ideas to avoid Unwanted Alarms by design. #1 REMOVE MANUAL PULL STATIONS (WHERE ALLOWED) The most-accessible method for an occupant to activate a fire alarm system is with a manual pull station. The IBC (most commonly-adopted model code in the US) has exceptions to remove manual pull stations for fully-sprinklered buildings. When this exception is offered, it’s worth considering. Many new construction projects require fully-sprinklered buildings anyways, so eliminating the exposure for a pull station in a highly populated area would reduce the potential for pranks. That being said, always consider the alternative. Are we talking about a middle or high school situation, or a hospital? Is it a dormitory, which is all-but-guaranteed to have a 2am alarm activation during Finals week? Or is it a critical care facility where there are multiple patients who cannot self evacuate? Manual Pull Stations do have their purpose and place in the industry; so we still want to consider the context and purpose for them. One important note that’s often missed – using the exception to remove manual pull stations doesn’t remove all of them in a building. One pull station must still be installed “at an approved location,” just not at all exits. #2 USE DUAL-ACTION PULL STATIONS If we can’t, or don’t want, to eliminate manual pull stations at all exits – then let’s think about securing them. Can we make the pull stations a little more involved to activate? Would going from a single-action (just pull down) to dual-action (push in and pull down) help prevent accidental activations? It’s possible, though I personally haven’t seen data to suggest it. I can’t imagine a teenager being discouraged by a minor additional action if they already plan to activate a system. But could it prevent a tall and curious five year old from activating the system? Possibly. Going from single-action to dual-action isn’t a notable cost difference, so this would be fairly easy to execute. If you have data on this – be sure to chime in in the comments. #3 PIEZO COVER FOR MANUAL PULL STATIONS Now “Prank” isn’t a formal term here, or at least not yet. But many of my personal experiences with false alarms was during college in the dormitories. How can we make activating a pull station troublesome for someone who is actively looking to empty a 1,000-person dormitory as a “prank”? One way is to put covers with a piezo alarm on the pull station itself. The piezo buzzes as soon as the cover is lifted, which draws attention to the location. If someone is activating the system during an actual fire, the logic is that they shouldn’t be deterred by a buzzer. But someone who’s trying to “get away” with something? Maybe the attention is a deterrent. Can using a Lift Cover with local Piezo alarm discourage malicious alarms? #4 VIDEO MONITOR PULL STATIONS AT EXITS Perhaps a better long-term solution isn’t a buzzer but a security camera at the location. If exits are already being monitored for security in that area, why not get a camera placed to include the pull station? If it’s much harder to avoid discipline, perhaps the security camera acts as a deterrent. While this might sound expensive – just imagine how many malicious alarms happen in some occupancies? The cost, time and effort of fire departments responding to calls that should have never been placed in the first place? It’s extremely disruptive and very well could lead to fines too. Addressing some of this upfront, when the building is being designed or renovated, could have lasting financial benefit to the owner. #5 SIGNAGE AT MANUAL PULL STATIONS Along the line of logic for security cameras – what about the threat of security cameras? Even just basic and clear signage right above the pull station of “SMILE, YOU’RE ON CAMERA” would be an inexpensive but potentially effective way of deterring bad players. Having a reminder for consequences may just be as effective even if a camera is not actively recording. If you’re a graduate student and looking for a research paper – maybe test this out and let us know. #6 SMOKE DETECTOR LOCATION Thus far we’ve focused on manual pull stations, and that’s because they’re the most easily-recognized way for anyone to activate the system. But what about the nuisance alarm? Perhaps the most front-of-mind false alarm is burned popcorn activating a nearby smoke alarm. Why is that smoke alarm there in the first place? Can locating required floor-level smoke alarms further away from cooking appliances help prevent nuisance alarms? Well, typically in homes, smoke alarms are required within sleeping areas, just outside of sleeping areas, and on each floor level. Similar requirements are found for residential occupancies. The IBC is explicit in the areas that need smoke detectors or smoke alarms in Section 907.2.
If a smoke detector is required in the area, how can we improve the situation? Can we shift the location to be as far-away from cooking sources as possible, but still be along the path of egress that we’re seeking to satisfy the IBC and NFPA 72? Many times it seems that during design, the smoke detector is just a hex with an “S” on it. It’s just a symbol that gets popped wherever there’s blank space on the CAD plan (I’m guilty of this). We need to be better than that. If a smoke alarm or smoke detector is anywhere near cooking appliances (stoves, microwaves, ovens) – then let’s get those detectors further away but still meet code. That extra distance means that normal cooking exhaust is going to diffuse and be less likely to trigger the smoke alarm. Here again – think about context, what we’re monitoring, and what we’re trying to achieve with the detection in the area. #7 USE THE UL 268 7TH EDITION One of my favorite improvements concerning smoke detection is that the UL 268 Standard for Smoke Detectors for Fire Alarm Systems, recently added a specific test, informally called the “Hamburger Test,” that requires a smoke detector or smoke alarm to not activate under specific cooking conditions. On a side note, the 7th Edition also includes a test for correctly responding to burning foam, which better matches modern furniture padding material. These additional requirements have come into play with the 7th Edition, which is now mandated for newly manufactured smoke alarm and smoke detectors. This is a huge step in the right direction to trigger less nuisance alarms. If we have the opportunity to install or specify UL 268 7th Edition detectors, that might be a major value-add for the owner. I don’t know the current status of availability or whether the manufacturers have caught up to the requirement yet, but the 7th Edition of the standard is currently mandated for new devices. YOUR EXPERIENCE What tips do you have? What are some practical considerations you make when designing or reviewing fire alarm systems? If you’re an AHJ, consider kindly advising owners or designers to consider these things by passing along the “lessons learned” can have a tremendous value to the owner. They can say no where it’s not code-required, but having been in the consulting space I’m incredibly appreciative of tips to consider that is in the interest of the owner. Comment below with your tips or ideas that you like. As always, thanks for being part of the community here!
6 Comments
Awhile back I wrote a piece on sprinklers in electrical rooms. At the time I was asked relatively frequently about when sprinklers are required or allowed to be omitted in electrical rooms. I guess intuitively, we recognize that electricity and water don’t mix well. We don’t want to address one problem (fire) by creating a new hazard (electrocution) with water in areas that it doesn’t have to be. In principle, I personally have just about always provided sprinklers in electrical rooms unless they were specifically requested not to be provided by the owner or AHJ; and in those cases, I followed the code path in the IBC or NFPA 13 accordingly. It seems as though the premise behind not including sprinklers is when the type of electrical equipment present a relatively low hazard or fuel source, and there is no storage. In that situation, a combination of 2-hour fire-resistance-rated enclosure with approved fire detection (assuming a smoke and/or heat detector here) will mean that a fire within the room will be recognized, and the rest of the building will not be compromised as a result. Providing pipe within an electrical room isn’t always an easy feat. NFPA 70 tells us that electrical equipment requires dedicated zones, and pipe shouldn’t be run above panels without drip pans or other methods of avoiding drip hazards above electrical equipment. Now are sprinklers in electrical rooms problematic? Generally not (in my experience). Can pipe routing be made to avoid electrical equipment? Usually yes. I try to only run one branch line into the room, most often above the door (since no electrical equipment is on the door), and stick pipe only above walking pathways within the room. Does the code or standards express any concern or guidance on this? Yes, both the IBC and NFPA 13 address the situation. One line that is included in the IBC specifically says that sprinklers “shall not be omitted from any room merely because it...contains electrical equipment”. To me, that’s a fairly explicit way of suggesting that the presence of electrical equipment alone isn’t a justification for omitting sprinklers. Now there are code allowances and necessary provisions to do so, but the suggestion is not to simply avoid sprinklers just because there is electrical gear. Despite it being awhile since that article, I have had a few requests to make this one into a flowchart, which I’m happy to present today. A special thank you to Alex Riley, PE, who contributed to the code research for this flowchart.
Wow a lot has changed in a week. We're holding on fine here, but I hope you and your family are safe and healthy wherever you are. Now back to more fun things like fire protection - After last week's debut of fire sprinkler requirements for elevators, I had a couple emailed requests for a fire alarm version. I love the idea and put some time into reviewing and organizing the requirements on the fire alarm side. This first iteration is a draft, and if you're well versed in this arena I'd love for you to take a look and let me know what you think. Feel free to email me directly at joe@meyerfire.com, or comment on it here. In the upcoming week I plan to incorporate ASME A17.1 and it's impact on the fire alarm side of accounting for elevators, hence the big [DRAFT] watermark on this PDF. Click on the image below to get a PDF copy of the Fire Alarm Elevator Cheatsheet: If you know anyone that could benefit from this content, please consider forwarding them a link. Hope you have a safe and healthy rest of your week! Thanks for reading. On every project containing fire alarm design I come across the same question repeatedly - does this unit require a duct detector? In short, there's two prevailing standards that determine whether duct detection is required. The first (and most common in the United States), is the International Mechanical Code (IMC). Section 606.2 identifies areas where smoke detection is required for the purpose of mechanical unit shutdown. The other prevailing standard is NFPA 90A, the Standard for Installation of Air Conditioning and Ventilating Systems. I'll address those requirements in a later post. Back to the question at hand - there's essentially six different scenarios a mechanical unit can fall into under the International Mechanical Code. These do not include the requirement for multi-level duct risers over 15,000 CFM, but rather whether an individual unit requires detection at the unit. Here is a quick cheatsheet summary concerning those scenarios: If you review or design fire alarm systems regularly, take a look and let me know what you think. If you know someone who might also benefit from cheatsheets like this, send them a link or tell them to subscribe here. Hope you find this helpful and have a great rest of your week! It is a popular and well-established concept that water and electricity don’t mix. Water is electrically conductive which creates a major hazard of electrocution where a continuous pool of water meets a live electrical feed. Can We Omit Sprinklers in Electrical Rooms? On a few occasions I have come across building authorities and building owners who assume that sprinklers will not be installed inside traditional electrical rooms. Why? The basic tenant that water and electricity don’t mix. While the concept is important, the intent of sprinkler protection throughout a building is not just for each item within a building, but the building itself. The primary intent of sprinklers is suppression – or stated differently – to prevent the growth of fire from the room of origin throughout a building. This includes all the rooms and spaces beyond just the electrical room where a fire could begin. This week I’m digging into guidance surrounding electrical rooms. NFPA 13 Guidance
NFPA 13 (2002 Section 8.14.10.3, 2007-10 8.15.10.3, 2013 8.15.11.3, 2016 8.15.11.2, 2019 9.2.6) allows sprinklers to be omitted in electrical rooms, but only where each of the following are met:
Concerns with Providing Sprinklers in Electrical Rooms Providing sprinklers within electrical rooms could:
Historical Approach Prior to the 1994 edition of NFPA 13, important electrical equipment were required to have hoods (or shields) comprised of non-combustible construction to prevent direct contact by sprinkler discharge. All electrical rooms were required to be sprinkler protected. Beginning with the 1994 edition, NFPA 13 introduced language to address concerns for firefighter safety and equipment damage. Sprinklers could be omitted in electrical rooms where the room contains dry-type equipment (no oils), is dedicated to electrical equipment only, is fire-resistant to reduce fire spread, and the room has no storage hazard. The 2016 Edition, the requirement for equipment hoods or shields was removed to direct it under the scope of NFPA 70. Just recently for the 2019 Edition new text was introduced such that no storage is permitted (non-combustible storage had been allowed) and liquid-type K-class (less flammable, non-spreading fluids) would be allowed. International Building Code Input The International Building Code (IBC) does not allow the omission of sprinklers “merely because it is damp, of fire-resistance-rated construction, or contains electrical equipment” (IBC 2000-18 9.3.1.1.1). Within the same code section, the IBC does allow sprinklers to be omitted in “generator and transformer rooms separated from the remainder of the building by walls and floor/ceiling or roof/ceiling assemblies having a fire-resistance rating of not less than 2 hours.” These rooms must have an approved automatic fire detection system. According to IBC commentary, buildings with sprinklers omitted in one of the sections allowed by the IBC would still be considered fully-sprinklered throughout and in compliance with the code and NFPA 13. This distinction is important as it carries eligibility for code alternatives, exceptions and reductions. Today’s Consensus Combined, both the IBC and NFPA 13 require electrical rooms to be protected unless the prescriptive alternative option is followed. As NFPA 13 commentary outlines, sprinkler systems have been successfully installed in rooms containing electrical equipment for over 100 years with no documented instances of a problem. While still seemingly controversial, most projects designed today include sprinkler-protected electrical rooms. Get More If you enjoy these articles, subscribe here. If you're already a subscriber, consider forwarding to a colleague. MeyerFire is all about dissecting real challenges that real people face in fire protection design. I'm thrilled you're a part of our journey for better fire protection worldwide. When I was six years old, I came home from school unexpectedly excited one day. I ran up our driveway, pushed wide the door and yelled to my mom. “You won’t believe it! There’s this place at school where you can go through shelves and shelves of books and pick out anyone you want – and it’s free! They call it a library.” It wasn’t one of my mom’s proudest parenting moments, but in our house, we never pretended to be great readers… or apparently even pretended to introduce kids to a library. I guess I’ll just come out and say it… Both of my parents are accountants. Now, I know what you’re thinking, and yes, the accountants are where my well-rounded sense of humor comes from. But there’s another big benefit to having parents as accountants – and it’s having a love for spreadsheets. I’m not sure if little excel formulas naturally run through my veins or whether it was every family calendar my parents ever created, but one way or another I thoroughly appreciate the power a spreadsheet has. Even if your parents are not both CPAs, there’s a place for Microsoft Excel in your engineering life. Excel isn't just made for your uncle accountant anymore - there's potential any engineer can love. For one, Microsoft Excel is not called the “Swiss Army Knife of Software” for naught. Excel is a blank canvas for any calculation you need to make. You can quickly create and repeat repetitive calculations to speed up and organize your workflow. You can complete reports, forms, create charts, tables, organize content, or use any of a myriad of highly powerful tools. Here are a few of my most often used formulas:
That’s pretty much all of my secret sauce. About 95% of the tools created combine those formulas alongside mathematical operators (like max(), min(), sin(), sqrt(), etc.). One of the best parts about using Excel is that you may already have access to it. If your company has a Microsoft Office suite (or what’s now their subscription model with Office 365), you already have access to these tools. Creating helpful resources is what we’re all about, and Excel is the epitome of giving you, the rockstar designer or engineer, the ability to create and flourish with the tools you need. You didn’t get into the industry to do poor, sloppy work. You came here to help save lives. We shouldn’t have to wait for programmers to create the daily tools we need to do great work. Excel is one way you can organize and validate the great work you do. There came a point near the end of my undergraduate work and at the beginning of graduate school where I realized I needed to create a clean, organized method to show details within calculations. The method I slowly developed needed a single logic path, had to be easy to follow, would thoroughly explain the process, and had to allow the easy repetition of the work. What’s resulted is the standard format that’s used in the PE Prep Guide and on many of the tools you’ll see around this site. Concepts are researched, painstakingly created, tested, refined, tested, refined, beta tested, and refined more. Standard formatting for MeyerFire tools - note the equations and worked examples with references cited. If you’ve followed the blog for a while, you already know the blog, daily forum, and even the PE prep materials are all created to help foster discussion that leads to shared expertise and knowledge. Outside of a few major players and organizations, the fire protection industry is comprised of thousands of thousands of small outfits that welcome this shared expertise. Our industry thrives on the contributions from a wide spread of individual parties. Don’t let me or anyone else douse your enthusiasm to create resources that improve your ability to impact the industry. Keep on keepin’ on. Oh and remember to take your kids to the library. I've heard from a handful of people to be sure to explore topics other than just fire suppression. I agree! There will be plenty more to come. It only seems appropriate after discussing the fire suppression cheatsheet and the code call cheatsheet in the last few weeks to also compile the latest cheatsheet I have for fire alarm design. Here's a blank cheatsheet and an example: If you're already using the Toolkit this is now available for download with today's update. Just log in here to get it. Along with having all of your design decisions documented for a project (or flagging the open items still left to figure out), perhaps the most important piece is how quickly you're now able to record your notes. If you don't see the video recording below, click here for a YouTube video of how quick notes can be recorded. Share MeyerFire was created to help you shine in fire protection. Know someone who might be interested in these tools or articles? Email a friend with a link today. Thanks for being a part of the effort towards better fire protection! Unless you're tuned in as an AHJ yourself, you've likely made a few "code calls" to a code authority and asked a litany of questions to make sure your project's design meets the local requirements. I'm not even sure if the term "code call" is a common term, but I've heard it enough that I suspect you already know what I'm talking about regardless of where you call home. I enjoy this process now, but I didn't always. Fresh out of school I'm pretty sure I was visibly shaking the time I first made a code call. I was sure that within seconds my cover would be blown and it would be all too obvious that I had no idea what I was talking about. Despite my awkwardness (I make a good engineer, right??) nothing went sour and since then I've slowly learned and repeated many many times. There was even one of my favorite code calls that I made about an elementary school to coordinate local fire alarm requirements. It was only right after the call late on a Friday afternoon that I found out that the fire marshal I just spoke with was hired onto our team and was starting the following Monday. They say fire protection is a small world, right? He turned out to be one of the most knowledgeable people I know and one of my favorite people to work alongside. The Joys & Pains of Code Calls Code calls also come in many different flavors. Sometimes I'm just shocked by how friendly and helpful code authorities are. I once made a call at 15 minutes till 5pm on a Friday to a small town in Arkansas, thinking I would just leave a voicemail. After my questions, I asked if the department conducted flow tests, and while he said they did, he apologized that because of a prior commitment he couldn't do it then but would be happy to do it first thing Monday morning. I almost fell out of my chair. Very helpful and caring people in this field. On the contrary, sometimes the hardest part about a code call is just finding the right person to speak with who is actually responsible for plan review of fire protection systems and getting a few minutes of their time. Not to pick on New York City because I love the people there and speak with a handful of you regularly, but if you're trying to get a hold of someone to verify or coordinate a few particulars of your system... well... good luck! Maybe it's because they knew I can't stand the Yankees. I also sometimes get AHJs who simply say all they do is 'per code' and they aren't interested in talking specifics. The whole point of the call is filling in the gaps where a code or standard does not direct but rather defers decisions to the AHJ. Want a siamese fire department connection with national thread, or a Storz-type? Either way is code compliant. As an engineer I can make either way work. Is a wall-mounted FDC permissible, or does it need to be freestanding? Either location is compliant, but NFPA 13 says the location needs to be coordinated with the AHJ. The Cheatsheet What I've gathered and refined over hundreds of code calls is my cheatsheet I currently use today. Just like the design cheatsheet, if you're using the Toolkit you can quickly highlight categories for your record keeping. What's even better about this tool, though, is that you can quickly fill in the content (while on the call) and then right after save as a PDF and email to the AHJ themselves. Want them to have a record of the call and a quick way to verify your notes? Great! You now have a logged code call and the AHJ has an opportunity to review your notes. The process of calling, taking notes, and composing the email used to take close to an hour total. This tool alone brings that total time to about 15-20 minutes. That's three-quarters of an hour you could save on every job you make the call! A Radical Big-Picture Concept One of my longer big-picture ideas to help the industry is to beta test and, if successful, open up a larger code-call database. I envision this as a database that brings designers and code authorities together to make local requirements clear and help jurisdictions get installations that reflect their preferences and mandates. Want to know what hydraulic safety factor is required for sprinkler systems in Springfield, Illinois? Great - a quick query in the database reveals that and a clean list of other local requirements. Want to know what type and location for FDC's that Tucson, Arizona requires? Great, we'd have that too. This would clearly have a huge value for designers and engineers - but what I'm really curious about is how to incentivize code authorities to take the survey or help us populate the database. If you're an AHJ, email me (jdmeyer@meyerfire.com) or comment below about whether you'd be open to the idea of making your local requirements public in a database. I would have to think that AHJ input would only help local authorities get installations that match their needs - but I also know that getting action out of anyone is only possible with mutual benefit and sometimes incentives. Just like the Design Cheatsheet posted a couple weeks ago, this form is integrated into the updated version of the MeyerFire Toolkit ready for download today. Below is a blank and filled-in template.
If you're already a Toolkit user, you can download the code call cheatsheet today by logging in here. If you're not using the Toolkit, you might consider joining in on what's quickly becoming what some consider the best tool for fire sprinkler design under $200. See more about it here. The Questions on My List The current code call checklist I use today has had items added and scratched over years of finding out what's important and what questions always get the same answers. That being said, there's no real one defined list that matches everyone's preferences. What questions do you ask that you feel are important to the design that's not explicit in code? Comment below. Join the Cause Our line of work in helping save lives and property is extremely important, but you already know that. This site is built to help you excel in fire protection. If you're not already subscribed to these free weekly resources & articles, you can do so here for free. I had several long standing global concerns when I was in grade school. It wasn't general anxiety or depression-related, but I certainly felt as though the weight of worldwide issues hung squarely on my small shoulders. At the time in school there was a major focus on the environment (I would imagine there likely still is now). It wasn't just a hard-sell on earth day, it was the disappearance of rain forests, erosion due to overbuilding, overpopulation, oil spills, our reluctance to recycle, and the overzealous use of oil that would undoubtedly cause our planet irrevocable damage. It was our generation's tasks to make right what generations before had begun. The gravity of the concern didn't feel just environmental either. New media opened the front door to war, disease, and a myriad of reasons to be pessimistic about the future and the world our kids will someday inherit. Now years later, as a father, I've heard similar sentiments prevail; "how could someone bring a child into the world today?" "I can't imagine how to parent with all the (fill in the blank) going on today." "Will there even be X around when our kids are old?" I'm not going to pretend that everything is sunshine and roses for everyone. There are major geopolitical issues and wars and famine and poverty and disease. A great day for me could also be the worst day for someone else. What I am hear to say is that when you adjust your focus from the immediate present and look out a just little more distant - there is so much promise in the world. And by so much promise I mean that the planet is getting healthier, cleaner, and the quality of human life is improving in ways that we've never seen before in human history. There has actually never been a better time to bring a child into the world. In Peter Diamandis and Steven Kotler's 2012 bestseller "Abundance: The Future is Better Than You Think", an author and engineer review historical data and trends that show how technology is achieving exponential improvements in computing, energy, and medicine. This bestselling book details many eye-opening reasons for optimism with the trends our societies are experiencing. These independent technology-based innovations have and will continue to drive major improvements to clean water access, food, energy, health care, education, and other facets of a first world standard of living for the planet's future nine billion people. Not only does mainstream media not cover the positive trends in the world today, but the future of our planet is looking more urbanized, education, cleaner, and healthier. Speaking of population, the United Nations recently released a DESA report projecting nearly 10 billion people in 2050 and over 11.2 billion people in 2100. Since this latest update there's been fairly widespread disagreement about these figures, with many researchers speaking out out about the projections that hinge on one major flaw: population growth rates are declining. Some countries have already peaked in population and are now in decline without immigration. Many expect that we, as a planet, will never reach more than 10 billion people. This isn't news to you if you live in Europe or Japan, of course, but in the U.S. many of us seem unaware of this major global trend. Research shows that with urbanization and better education, couples have less children. This speaks to major positive impacts in using less resources and shaping a cleaner planet in the future. Trends in Fire Protection That's great Joe, but what does this have to do with fire protection? First, as is my underlying theme in the whole website - engineering is going to save the world. I'm sure my wife would also suggest that scientists deserve some credit too, but this isn't her blog. Second, don't be discouraged if you feel that the quality of our line of work is in freefall, that no one is entering the industry, or that we've lost all sense of pride in what we do. Big-picture trends in fire protection are very positive, with death rates due to fire steadily decreasing per capita over the last century. The unrelenting overall trend is that we are doing something right as fewer people per capita are dying now from building fires. Fire fatalities have been and continue to decrease with advancements in code adherence, our knowledge of fire protection, and shared education of the subject. Just the last 30 years across Europe and the US there's been major improvements in fire safety: Global trends in fire deaths have decreased over the last quarter-century as shown in this US FEMA study. Third, if you've ever felt similarly barraged by the negativity in the media or fears that we're only one step away from global catastrophe, I would wholeheartedly encourage you to read or listen to the book Abundance: The Future is Better Than You Think. There's no summary that I could put together that I feel would do the book justice. Of the fifty-plus books I read last year this was without-a-doubt the most impactful. [On a side note, if you're wondering how I average 50 books a year - I cheat and listen on audible.com. You can actually get the book Abundance and another book, for free, with a free trial here] If you've read Abundance, comment below on your impression. If not, I'd highly encourage you to read it and let me know what you think (shoot me an email at jdmeyer@meyerfire.com). I promise the read will be worth your time. Similar Articles If you've enjoyed this article, consider subscribing to these free weekly posts here. Here's a few other book reviews: Chicago Death Trap: The Iroquois Theatre Fire of 1903 Fahrenheit 451 & The Thirst For Knowledge Triangle: The FIre That Changed America References Diamandis, Peter H. Abundance: the Future Is Better than You Think. Simon & Schuster, 2015. Fire Death Rate Trends: An International Perspective. FEMA, July 2011, www.usfa.fema.gov/downloads/pdf/statistics/v12i8.pdf. United Nations Population Division | Department of Economic and Social Affairs. United Nations, www.un.org/en/development/desa/population/publications/trends/population-prospects.asp. What's not to like about a Top 10 list? If you know someone who may enjoy reading about this, please consider forwarding to a friend. Here's the top ten most popular articles and posts in this past year:
I hope you've had a great 2018 and are looking as forward to the coming year as I am.
If you've found any of this helpful, consider sending this to a friend or encouraging them to sign up for these weekly articles here. Thanks in advance and have a great holiday and happy new year! |
ALL-ACCESSSUBSCRIBEGet Free Articles via Email:
+ Get calculators, tools, resources and articles
+ Get our PDF Flowchart for Canopy & Overhang Requirements instantly + No spam
+ Unsubscribe anytime AUTHORJoe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About FILTERS
All
ARCHIVES
March 2024
|