We have a fire pump room which is very constrained.
NFPA 20 (Edition 2016), A.4.21.1.2 (2) For horizontal split-case fire pumps, there should be a distance of not less than 10 diameters of suction pipe for side connection (not recommended) to the fire pump suction flange. The main pumps have a capacity of 3000 gpm (two are electrically-driven and two are diesel-driven) with two jockey pumps at 300 gpm capacity. All are in one room. Pumps suction and discharge pipe size is 12" as per Table 4.27 (a). In this scenario, what is the meaning of 10 diameters - is it 10 times of suction size diameter of pump (means 10x12= 120") or something else? Why is this requirement only limited to suction and why not for discharge side as there is tapping for pressure monitoring? Any thought would be much appreciated. Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
39 Comments
Wayne Ammons
6/29/2020 08:03:44 am
The purpose for the 10x distance is to prevent turbulent flow from entering the fire pump and impeller which can cause wear and cavitation over time. If your suction size is 12 inch, you will need 120 inches from the fitting flange to the pump suction flange or suction fitting flange, depending on the configuration. Figure A.4.15.6 of NFPA 20, 2016 edition shows example diagrams to better explain this.
Reply
6/29/2020 10:11:07 am
Does the same hold true for all suction pipe sizing's ? So that a 4" feed pipe would require 40" of straight pipe before the pump and no fittings (90's, 45's etc) in that 40" space ?
Reply
Casey Milhorn
6/29/2020 10:28:28 am
So the 10 pipe diameters, from memory, only applies to backflow preventers and fittings that are at a right angle in a horizontal plane to the suction of the pump. If your underground lead-in is lined up with the fire pump and your only change of direction is in a vertical orientation, you can have less than 10 pipe diameters. Vertical changes in direction don't cause nearly the same type of issue as a horizontal change in direction due to the way gravity affects the fluid moving through the piping. Horizontal changes of direction cause the water to rotate and have the possibility for turbulence and air pockets. 6/29/2020 10:46:20 am
10 x the pipe diameter related to the length of the proposed pipe the length has to be at least 1X the diameter of the proposed pipe. I have seen a pump that was piped directly in from the side.
Reply
Thomas Jones
6/29/2020 11:27:19 am
As mentioned, it is for turbulence. One thing I have done in tight pump rooms is create a "n" shape. So from your incoming line go up than change direction down for 10x the pipe diameter.
Reply
Shaikh
6/29/2020 11:43:18 am
If there is case where o & Y gate valve has to be included within this 10 times pipe dia of suction, Do we need to exclude this length of O & Y gate valve.
Reply
Nguyen Thong Nhat
6/29/2020 09:06:43 pm
Disagree, 10 x Diameter requirement apply only for tee and elbow, or any fitting that cause water turbulent in suction pipe, OS&Y valve isn't one of them.
Franck
6/30/2020 02:08:42 pm
If OS&Y valve is provided, no need to maintain this 10 x diameter as there is no obstruction, i.e. no turbulence, within the pipe when the valve is open.
Sunil kumar
6/30/2020 11:54:42 am
Jockey pumps requirements are based on local client preference, so it is 300 gpm in this case.
Reply
Shahad
10/13/2020 05:03:08 am
Technically, the jockey pump capacity should be less than the flow from any sprinkler head in the system. In the event of fire, Primary fire pump MUST turn on. This is one of the reason why NFPA doesn't mandate jockey pumps to be listed, as its function should be limited to maintain the pressure in the system.
Nguyen Thong Nhat
6/29/2020 08:52:06 pm
...there "should" be... It's mean you can follow or not follow it. Because Fire pump often run in a short time, so, if your pump room is small, you can pass this requirement. You also can find the explain that why it's should be 10x Diameter in ANSI/HI 9.6.6 figure 9.6.6.3.3b
Reply
Nimal Tissa Wijetunga
6/30/2020 07:41:47 am
Disagree. 10 pipe diameter is a requirement as per NFPA and FM Global.
Reply
Nguyen Thong Nhat
6/30/2020 09:40:33 pm
Yes, I think there is an error of word in that requirement. it must be "shall" instead of "should", as shown in 4.16.6.3.1 and 4.16.6.3.2 (NFPA 20-2019 ed.). By the way, there are many commercial building having a small area for pump room that seldom seen in industry building, and they also needn't the FM approval.
Franck
6/30/2020 02:10:54 pm
This is a reliability issue.
Reply
koray uluç
6/30/2020 03:01:11 am
The concern for 10 pipe diameter straight line requirement is not turbulence nor cavitation. it is for the differential pressure occurrence on each side of the pump impeller. That is why it is not required for end suction pump but required for horizontal or vertical split case pump only.
Reply
Franck
6/30/2020 02:14:11 pm
end suction pumps are normally not allowed by NFPA, only horizontal split case pumps (more robust and more reliable).
Reply
koray uluç
7/1/2020 01:36:32 am
Sorry, but this is a wrong info
Franck
7/1/2020 01:50:43 am
As often, I was too much self confident and the information I put was wrong (end suction pumps can be FM approved and UL listed). Mostly based on my European experience where such pumps are very often provided, and almost never UL listed or FM approved.
Nithin Babu
6/30/2020 06:58:22 am
If space is constrain in pump room, then the requirement of 10 D can be satisfied by introducing diffuser, i remember victualic offer such diffuser
Reply
Jeva
10/7/2020 07:18:23 am
Hi can I know the type of diffuser.
Reply
Franck
6/30/2020 02:19:28 pm
In addition to all the above comments, your question was also "why we don't have the same requirement on the discharge side ?".
Reply
6/30/2020 04:31:32 pm
The Minnesota State Fire Marshal used to publish a great one-page newsletter named "Quick Response." The June 2008 issue covered Fire Pump Suction Piping Arrangement. It can be found at the link below. Keep in mind the NFPA 20 references were from a previous version of NFPA 20.
Reply
Nimal Tissa Wijetunga
6/30/2020 10:46:29 pm
Within that 10 Pipe diameter distance, only OS&Y Gate Valve is allowed and this 10 pipe diameter is to get laminar flow to the impeller from the suction side and it is definitely a requirement.
Reply
JUHWAN KANG
7/1/2020 01:50:19 am
Could you inform where can I find any clause for that OS&Y Gate Valve is allowed within 10D?
Reply
Franck
7/1/2020 04:31:05 am
NFPA 20 (Last Edition)
Nimal Tissa Wijetunga
7/1/2020 10:27:15 am
Dear Franck,
Reply
Joe Meyer
7/1/2020 11:21:36 am
Nimal, you need to reply in the correct string and also comment specifically about what your concerns are. This forum is for fostering discussion.
Reply
Franck
7/1/2020 11:38:56 am
Dear Nimal
Reply
cy
7/1/2020 11:19:04 am
You can review the section for suction diffuser, which according to the NFPA 20 ed 2019 is equvalent to the 10 pipe diameter of straight pipe. Bue review the equivalent pressure loss for this device and check with the manufacturer the installation requirements
Reply
Mohammad
2/8/2021 03:38:08 am
Dear gents
Reply
Ruben
6/25/2021 10:31:06 am
Would the 10 times pipe diameter requirement be applied to vertical inline pumps?
Reply
Todd Delisle
7/23/2021 08:17:15 am
No it would not. (must maintain appropriate size and prevention of trapped air)
Reply
Fidencio Gomez
10/27/2022 04:22:29 pm
Todd good afternoon where did you find this at.
Carlos Segura
11/12/2021 11:53:51 am
Regarding suction diameter, NFPA says that on 4.16.3.2 says "The size of that portion of the suction pipe located within 10 pipe diameters upstream of the pump suction flange shall be not less than that specified in Section 4.28." but what happen for the rest of the pipe?, what size I have to choose?, For example a 1500GPM pump according with table 4.28(a) could be connected to a 8" suction pipe, but only for the 10XD pipe portion, right?, sholud the rest of pipe follow the rule of thumb to use a equal or one bigger size pipe than pump suction?
Reply
Wyn Hinkel
12/14/2022 12:05:10 am
Pretty sure the vertical drop is included in the horizontal distance of 10 pipe diameters before suction flange.
Reply
Ozzy
2/21/2024 01:15:31 pm
I agree with you. According to nfpa 20 2019 the 10 pipe diameter requirement includes vertically fed pumps
Reply
Vasanthan
2/10/2023 12:12:25 am
For a horizontal split case pump, 10D straight pipe to be provided for the suction inlet. My design includes a gate valve and strainer in the 10D. Is the strainer allowable in 10D? Unable to find in NFPA 20 any input on this.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |