We are inspecting an existing fire sprinkler building for an upgrade to an Extra Large Orifice (ELO) system.
We performed a hydrant flow test and noticed a 14 psi static loss between the hydrant, 185-ft of 8-inch ductile, 2 elbows and 8 feet of elevation rise to the supply side of the RPZ backflow preventer. We recorded 73 psi at hydrant and 59 psi at the number 1 test cock on the RPZ while static. I spoke with the water authority and they confirmed no meter or check valve on the 8" fire line; it is straight into the valve room plus 2 elbows. The building is 20 years old and the pump test provided 120% of rated capacity. Any idea how the static pressure inside the building is 14 psi less? Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
18 Comments
Dan Wilder
1/8/2021 08:27:30 am
Check your gauges for calibration and try to use the same type for both. Using a glycerin filled 100# and an Air/Water 300# will not be equal when comparing them.
Reply
Mike
1/8/2021 09:06:09 am
Check the gauges.
Reply
Andrew K
1/8/2021 09:14:46 am
I can only agree with previous responses. In general, we should consider the the pressure gauges as a possible source of psi discrepancy. I would offer that if you have the opportunity to use one certified pressure gauge for both locations, it may eliminate any discrepancies between different gauges.
Reply
Jesse
1/8/2021 09:30:58 am
First of all check the gauges. We've all seen way too many mis-calibrated gauges. If the gauges are good, it's likely the UG pipe is fouled. I ran a basic HW manual calc presuming a flow of 1000-gpm. Your friction loss is in the area 1.38 psi. Your 8-ft rise in elevation accounts for a loss of 3.46 psi for a total loss of 4.84 psi. You've lost 14 psi, so we're at the point where the culprit may be scale buildup on your UG pipe. If this is the case, you'll need to replace the UG.
Reply
Jesse
1/8/2021 09:37:41 am
Sorry - I just re-read the original post. Earlier my brain registered the pressure differences while flowing, not static.
Reply
Casey Milhorn
1/8/2021 09:38:51 am
Completely agree with checking the gauges. Also make sure you are doing them at the same exact time. Sounds like you are in an industrial area and water usage can spike up and down dramatically affecting the static pressure available, especially if the city water main is a dead end line and/or undersized. Other than that, physics is physics.
Reply
Franck
1/8/2021 09:56:56 am
For the same elevation, static should be the same everywhere in your system.
Reply
Glenn Berger
1/8/2021 10:13:24 am
After checking the gauges (easy answer), you might have underground piping that has a problem (internal or external). Do you know if there are soil corrosive issues?
Reply
Shane
1/8/2021 10:29:52 am
my best guess there is a small leak, due to corrosion, in the underground piping or at a fitting connection after the backflow.
Reply
C.T. Carbonari
1/8/2021 10:34:50 am
I always check testing equipment & methodology (i.e. gauges, connections, locations,piping configuration) whenever unexpected hydraulic anomalies occur.
Reply
C.T. Carbonari
1/8/2021 11:06:58 am
Also, this sounds like a Fire Service Main Flow Test (as opposed to a traditional hydrant test)
Reply
1/8/2021 02:42:32 pm
I doubt that all of the gauges are that far off. With the pump only flowing at 120% if the original was 150%, there is a flow restriction.
Reply
Felipe Pedraza
1/8/2021 07:09:22 pm
If the guages have been checked.and are of the same make and kind, proceed to checking all roadway valves near the source and make sure that they are fully open and in working condition. I have found some of them close and even broken in the past. Also check with utilities for any watermain repair near the area, or waterline taps to the main and the cut out line donut went into the main and is either blocking a watermain roadway valve ir is blocking the water at the BF.
Reply
Tony Brown
1/9/2021 08:22:30 am
I have come across this situation three times. Once was due to a throttled down curb valve, the other two was because a neighbor had tapped into my clients incoming service.
Reply
FRED WALKER
1/11/2021 10:08:11 am
1. Check gauges, ensure calibration, easy first check swap gauges.
Reply
C.T. Carbonari
1/14/2021 10:58:07 pm
I hope the OP responds with clarification when this issue is resolved.
Reply
Jesse
1/15/2021 07:40:17 am
Agree with C.T. Would be beneficial to all of us if the OP circled back with the resolution. Differential diagnosis are great, and this created some great discourse. We're all better at what we do because of it.
Reply
Mike Millman
3/2/2021 01:40:58 pm
1) Is it possible there is more elevation change than you realize? The ground can gradually slope quite a bit without really "feeling" it. Double check elevations using something like Google Earth Pro.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |