There is a confusing discrepancy between NFPA 13's ban on hanging 1.25" and greater pipe to bare metal deck versus the availability of UL listed anchors with a test load of 850 lb (that is the number for the 3/8" Sammy XP 20).
I don't understand how something that has passed such rigorous testing could be forbidden by the code. Does anybody have any background knowledge on this subject? On top of this, I don't understand the configuration required for this application by NFPA 13. It says anchorage needs to be provided by "punching the vertical portion of the metal deck and using through bolts." (2016 Ed. 9.2.1.4.1) I don't know how to visualize this arrangement and there are no details or photos in the handbook. Does anyone know what this is supposed to look like? I've tried reaching out to NFPA's technical resources and have not gotten a response. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments
Dan Wilder
2/18/2020 10:00:43 am
This was previously discussed in the thread below:
Reply
Nash
2/18/2020 10:38:18 am
NFPA 13-2019
Reply
Jonathan D Griffin
2/18/2020 11:00:03 am
Keep in mind, that the reference is not concerned that the supporting straps or bolts cannot hold the weight of the water-filled pipe; but whether the Roof Deck system is capable of supporting this load. And if so, what attachments may be utilized to attach the piping to the Roof Deck.
Reply
Anon
2/18/2020 12:06:16 pm
This is worded poorly in NFPA 13 and applies to “through bolts” not other listed hangers based on the gauge of metal. 1” is not the limitation.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |