Hello everyone -
I have a problem with two identical fire pumps rated at 145 psi at 2,500 gpm. When testing for 0% flow and 100% flow the pump gives the correct pressure, but, when testing 150% flow the pressure drops dramatically, it has to show 125 psi and the result is 92 psi. The pumps has a 10-inch flange suction an as NFPA allows it was installed a 10-inch pipe directly to the pipe, no suction reducer, having 16-ft (5 m) long of distance for one pump and 19'-6" (6 m) for another one, the second one with two 45-degree elbows installed more than 10 times the diameter from pump suction. The tank is 23-ft (7 m), full of water. The test outlet is installed on the other side of the tank, so the flow does not fall over the suction inlets. The antivortex inlet has a plate of 7.5 inches above the floor. The pump discharge is 10 inch. The flow meter is 8-inch diameter with 8 diameters before and more than 5 diameters after. Any idea why the pressure at 150% is so low? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
16 Comments
Mike L
1/18/2022 07:11:29 am
We would need to get a full description on how the whole arrangement is piped up. Are the pumps piped in parallel or in series?
Reply
Mourad
8/29/2022 05:51:54 am
I will highly appreciate if we can debate why 150% is required for centrifugal fire pumps if 100% is achieved
Reply
Dan Wilder
1/18/2022 07:21:32 am
Need to get the icosahedron of trouble shooting out....
Reply
Anthony
1/18/2022 07:29:27 am
Had to google icosahedron, not upset.
Reply
Martin Moffitt
1/18/2022 08:18:35 am
Me Too!
Dan Wilder
1/18/2022 08:23:13 am
Always nice to keep things light on the "most productive day of the week"...
Glenn Berger
1/18/2022 08:17:51 am
In addition to the above:
Reply
Alex
1/18/2022 02:54:11 pm
Million dollar question, Glenn. What did the factory show?
Reply
1/18/2022 08:22:14 am
We need a bit more information, but my gut reaction is that the suction pipe is too narrow.
Reply
Jesse
1/18/2022 08:33:52 am
I'd be curious to know more about the pump arrangement.
Reply
Cliff Schulze
1/18/2022 09:06:10 am
I assume you are getting the 125 psi from the factory curve? Otherwise, per NFPA at 150% of rated flow, you need to get 65% of rated pressure, which is 94.25 psi. The 92 psi you are getting is within the 5% variance allowed.
Reply
SCHULMAN
1/18/2022 09:59:43 am
I knew what a 20-sided dice was Dan ,,,
Reply
Franck
1/18/2022 10:03:06 am
10 in. suction pipe is fine and this should not be the problem.
Reply
Jack G
1/18/2022 04:11:06 pm
Agree with above.
Reply
Hello Everyone, thanks for all your recommendations, We are just leaving from the installation, At the end it was an air bubble that made up all the problem.
Reply
James
9/13/2023 02:36:17 pm
In the event to pressure cannot reach 150% and can only reach a pressure over 108%, is there a requirement on the signage for the pump room? Due to the city water supply the pump cannot reach the 150%, so is there a requirement to show this for future ITM?
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |