This question is regarding obstructions to residential upright and pendent sprinklers.
The 2016 edition of NFPA 13, 8.10.6.1.2 (4) states that obstructions that are located against the wall and that are not over 24 inches in width shall be permitted to be protected in accordance with Figure 8.10.6.1.2(c). This is a pretty sweet rule, as basically your only concern is the sprinkler distance from the wall and not the obstruction dimensions. However, the 2016 edition of NFPA 13R does not contain this wonderful rule, even though the rest of the obstruction rules are essentially the same. Any thoughts on why the decision was made not to include this rule in NFPA 13R? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Pete H
3/19/2024 06:51:28 am
Since we're just giving thoughts: if I had to hazard a guess it's because in residential situations we're expecting more common other obstructions to discharge (ceiling fans) as well as this rule's necessity becoming suspect due to the shadow area allowances and sidewall heads on an opposite wall allowing for 30" deep and wide soffits.
Reply
Anthony
3/19/2024 08:08:33 am
I think it's because residential sprinklers have a 'flatter' spray pattern so are more susceptible to obstructions protruding down from the ceiling. Also, the performance objectives of a residential sprinkler is to wet the walls to contain a fire to a compartment.
Reply
Colin Lusher
3/19/2024 08:29:40 pm
Except that the section regarding these soffits in NFPA 13 is specifically applicable to residential sprinklers only.
Reply
Dan Wilder
3/19/2024 09:19:25 am
Had to do a little digging as to the "Why"....and didn't find much unfortunately....but my guess is it wasn't submitted to the 13R Committee for approval....but.....
Reply
Chris Dorsey
3/20/2024 07:27:24 am
Thank you Dan. Good to know. So I guess in a couple of decades when our AHJ adopts 2022 we'll be good to go.
Reply
Jack G
3/19/2024 02:55:03 pm
As indicated above, I believe it’s because of the flat spray.
Reply
Mike
3/29/2024 08:18:35 pm
NFPA 13 and 13R have different intents as stated in, I believe, Ch. 1. Therefore different rules.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop March '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
April 2024
PE PREP SERIES |