NFPA 13 does not allow ESFR protection for shelf or bin box storage. I can see the logic, and this has been in the code for years.
However, FM Data Sheet 8-9 does allow ESFR protection for shelf and bin box. I can protect shelving up to 15-feet with 0.85 over 2,500 sqft but I can't protect it with K25 at 70 psi. Any insights on the logic here? Has testing been done that supports this one way or another? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
Dan Wilder
2/18/2022 08:57:20 am
My opinion...there are likely some op-ed's or research papers to this issue but I'll see if those with more storage experience can populate those.
Reply
Jesse
2/18/2022 10:19:52 am
Happy Friday y'all.
Reply
Franck
2/18/2022 12:06:06 pm
In the good old time, FM Global (know at that time as Factory Mutual), was using density/area values in data sheet 8.9 (as well as other data sheet in the storage section), and had other tables for CMSA (designated at that time as Large Drop... nostalgia, nostalgia... and for ESFR.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |