NFPA 24, Section 7.1.1.2 (2016 Edition), states that control valve shall be installed in each hydrant connection. What is the purpose of this control valve, other than facilitating maintenance? Would this be considered a "control valve" per NFPA 24 3.3.3, and does this have to be a post-indicating type valve? Common hydrant arrangement for illustration purposes. Based on my limited understanding, this control valve is just a post-indicator valve/isolation valve which is for shutoff when there is an impairment downstream. I'm trying to get a better understanding of its purpose. Thanks in advance.
Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
9 Comments
Jesse
7/10/2020 10:08:19 am
Its primarily for maintenance. And it doesn't necessarily need to be a PIV. I use NRS (non-rising stem) valves most often
Reply
Brian Gerdwagen
7/10/2020 10:38:17 am
This is also to turn off the hydrant after being hit by a vehicle. Some jurisdictions, like Los Angeles County, require that the control valve be a decent distance, like 15 feet, away from the hydrant for this purpose.
Reply
Sue
7/10/2020 11:11:27 am
We do not require a PIV at this control valve because the hydrant is so close. If the hydrant is not live, a street key can be used to open the valve.
Reply
Jimmy Landmesser, Jr.
7/10/2020 11:22:25 am
As stated previously, yes maintenance is a key component and the other being repairs. The intent is to avoid impairing more than that single hydrant when repairs or maintenance are needed. No, a PIV is not required.
Reply
SK
7/10/2020 12:17:31 pm
Thanks for all responses.
Reply
Sue
7/10/2020 12:34:43 pm
I sometimes agree with what you are saying SK. I worry about the end users costs.
Ken Thackery
7/10/2020 12:40:02 pm
HI, It's called a repair gate (NRS) and not required in every jurisdiction just depends on the site and water/fire loop configuration.
Reply
Bruce Verhei
7/10/2020 07:42:53 pm
1. Need for maintenance is sufficient cause to require a foot valve.
Reply
10/5/2020 06:41:37 am
Thank you for this valuable information. It is most appreciated.