I have a mixed-occupancy, 100-year old 1-story house within a metro area. There is existing office space up in the front of the building, and a one-bedroom apartment in the back.
We are adding a camelback addition to the building. The existing office space will remain as is and we will have two 3-bedroom apartments in the back. The camelback will be set back 20-feet from the front of the house. The height of the building will be 30-feet. Can I use 13R or 13D in the residential units? Do I need any sprinkler in the commercial office space upfront? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Anthony
10/22/2021 08:51:59 am
Reply
Brian Gerdwagen FPE
10/22/2021 08:55:51 am
If you are under a modern version of the IBC, you need to sprinkle the entire Fire Area containing a group R occupancy. So you must sprinkle the office(s), in addition to the reply above.
Reply
Jack G
10/22/2021 11:21:08 am
Yes, Brian.
Reply
Alex
10/22/2021 12:03:47 pm
Hi,
Reply
DanE
10/22/2021 12:26:31 pm
You can find some information here:
Reply
Todd Wyatt
10/25/2021 09:44:07 am
The Occupancy Classification(s) of the building per the applicable IBC determines the fire protection and life safety system requirements for those occupancies. There are (4) different Group R occupancy classifications: R-1, R-2, R-3, and R-4. The design professional classifies the occupancy(s) of the building with AHJ approval. IBC Chapter 9 identifies the general requirements for Group R as well as the specific requirements for the R-1, R-2, R-3, and R-4. NFPA 13 and NFPA 13R are references standards per the IBC that identify how sprinklers are to be installed, maintained, and inspected. The IBC is the scoping document as to where automatic sprinkler systems are required.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |