Where would I go to find CMDA protection of Rack Storage less than 12-ft?
In this particular case, I'm looking at Class III commodities on wire racks in a 2,000 sqft room with 8-ft ceilings. This is paper file storage. In the past, I have been able to use the miscellaneous storage requirements, but not this time. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Jesse
12/19/2023 08:07:37 am
This is effectively miscellaneous storage which is protected as OH 2. See 2016 NFPA 13 Table 13.2.1 - C-III Commodity <12-ft. Use the design curve noted in Figure 13.2.1.
Reply
Anthony
12/19/2023 08:19:57 am
Agree with Jesse here.
Reply
Eric R
12/19/2023 08:19:13 am
A quick caveat to add to Jesse's answer is that there is a difference between "miscellaneous storage" and "low-piled storage", and while the two are basically identical for lower hazard commodities they have completely different requirements for plastics storage.
Reply
Jesse
12/19/2023 01:19:00 pm
Agreed in the difference between low piled storage and miscellaneous storage.
Reply
sean
12/31/2023 06:08:15 pm
I think people move to misc. storage too often.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |