I'm working on an existing system in a seven-story building. There is an existing pump and piping which snakes its way through the building.
There is a pressure gauge at the inlet and outlet of the pump, but none afterward until 200' away from the pump room. The pipe branches off with a zone valve assembly with pressure gauge serving that floor area, and then upwards through the remaining floors with no gauge. Zone valve assemblies with gauges are located on the floors above. Now for my question - when performing hydraulic calculations, where would you indicate the "bottom of riser"? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
23 Comments
Glenn Berger
4/17/2023 08:09:43 am
Typically the base of the riser is where the water supply enters the building.
Reply
OP
4/17/2023 09:30:55 am
The service comes into the building and runs for more than a hundred feet before the DCVA, then probably around 75 feet to the pump inlet, then the 200 feet stated earlier begins.
Reply
Josh
4/17/2023 08:13:49 am
I'm with Glenn here. Typically I consider the base of the riser to be a standard 3' - 5' below where the base of the riser is from the supply in calcs to be safe. The frost lines I mostly work in are pretty shallow so it typically covers that too.
Reply
Eric R
4/17/2023 08:20:55 am
So going by the book, NFPA 13 considers each zone control assembly as the starting point for a "sprinkler system" assuming they have a control valve, gauge, flow-switch, and drain. If that is true then by the book you are required to hang a hydraulic placard at that location and that location would be your base of riser point.
Reply
Dan Wilder
4/17/2023 08:30:28 am
Definition of a sprinkler system within 13
Reply
chad
4/17/2023 08:46:11 am
Agreed and to add to that:
Reply
Franck
4/17/2023 08:45:06 am
As indicated by Dan and Eric, Base of Riser (BOR) is at the alarm check valve, where you put the placard
Reply
OP
4/17/2023 09:37:10 am
There are also no alarm check valves in the entire system, just water flow switches at the zone assemblies.
Reply
Ryan Page
4/17/2023 08:56:27 am
I mostly agree with Eric, except I would not use the pump outlet as the BOR. As he stated, by the book, the BOR would be at the supply side of the control valve serving the system you are calculating.
Reply
OP
4/17/2023 09:52:29 am
There is a standpipe as well that is served by the pump. The pipe tees off, and the standpipe routing is completely unrelated to the sprinkler piping. They don't share chases, or routes.
Reply
Eric R
4/17/2023 09:03:07 am
Longer Rant Incoming:
Reply
Ryan Page
4/17/2023 09:21:27 am
The flow and pressure needed at the calculation endpoint would be that of just one sprinkler. Calculations are based off demand, not supply.
Reply
Eric R
4/17/2023 10:43:00 am
Ryan,
Ryan Page
4/17/2023 09:27:56 am
Sorry, forgot to add that flow tests are required to be done within one year of submitting plans to the AHJ (I don’t currently have a copy of 13 in front of me so I cannot quote what section that’s from). So yes, you can do a preliminary design, but you will not be able to submit it for a permit.
Reply
Eric R
4/17/2023 09:41:24 am
I don't necessarily disagree with you, which is why I commented on the issue of base-of-riser flow testing not accurately taking into account outside hose requirements.
Dan Wilder
4/17/2023 11:47:07 am
Not sure how you're using a main drain to justify hydraulics...that test is to only show history of the water supply and trigger an investigation to a water supply piping obstruction/closed valve or possibly a new hydrant flow test. At that point there is enough information to start reviewing hydraulics within the building.
Reply
Eric R
4/17/2023 01:50:06 pm
(Dan, this wall of text isn't particularly aimed at you minus the aboveground piping part :) , it's just a hot topic of mine at the moment)
Dan Wilder
4/17/2023 10:03:38 pm
No issue documenting an issue on a separate form in addition to the standard NFPA 25 form however the main drain test does nothing to verify overhead design....it's there to be an easy check of possible underground or supply issues. Now with the forward flow testing for backflows, I would love to see the hydraulic BOR be placed there in the future (for in building or dedicated single building riser feeds at least).
Anthony
4/17/2023 09:17:53 am
The point of the BOR hydraulic point is so that your hydraulic placard that is hung on that riser can be examined and compared to the current pressure gauge on the system. When you preform your quietly main drain test/ water flow alarm test you can see if the residual pressure is greater than the system placard shows required. If the residual pressure is less than 10% of the requires system pressure then you have an impairment.
Reply
Eric R
4/17/2023 09:52:10 am
Anthony, you are on the right track, but it is important to clarify that technically you should not be comparing main drain results to the hydraulic placard.
Reply
James Art
4/19/2023 11:19:20 pm
Yes, a 2" drain is intended just to watch the water supply, and compared to previous tests.
Peter H
4/17/2023 10:34:23 am
For the full building? At the pump outlet.
Reply
Cory
5/25/2023 03:44:55 pm
I typically consider the base of riser as the zone control valve assembly as that is where you put the NFPA 13 calc plaque. Which would be after a fire pump, at the inlet to BFP or individual risers if you have multiple. I usually don't see base of riser's outside of the building/riser room.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |