NFPA 13, 2022 Edition, Sections 28.2.4.2.4 says to that a design area can be only the sprinklers within the available design area whenever the available floor area is less than the density/area size.
The next section, Section 28.2.4.2.5, says that when the total flow is less than the density x minimum design area, an additional flow (phantom flow) shall be added at the common point of connection. When do you apply one versus the other? If I am interpreting this correctly, you only apply the 28.2.4.2.5 when you have the available floor area, but not the minimum flow? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments
Pete H
12/8/2023 07:20:23 am
I think I'm having this conversation elsewhere and it's honestly making me think this is a conflict specific to NFPA 13 (2022 edition).
Reply
Dan Wilder
12/8/2023 08:18:32 am
Had to look up why the original change but here is the substantiation. I believe the interpretation was being applied to the far end of systems and not related to the actual tie-in point of the system being applied with the additional flow requirements (so off page to the right of Figure A referenced in 28.2.4.2.5) so it was proposed to change in the 1st draft of the 2022 edition, then discussed in E&S and other venues as to where it should be applied (on the end of the main feeding the area, the connection point of the feed main to another feed main, the remote end of the full system regardless of the actual tie in point for the area being calculated, I think even dividing the flow by the number of branch lines and adding that in at each point came up). Ultimately, the POC from the smaller system to the building system "proper" was passed in Public Comment No. 258-NFPA 13-2020 [Section No. 28.2.4.2.5] as to allow the system main feeding the smaller main the ability to support the larger area being calculated under the "Phantom Flow" addition.
Reply
Pete H
12/8/2023 08:33:51 am
Yeah.... I feel like a lot of headaches could have been avoided if they just changed the words to the connection point on the main closest to the calculated area.
Dan Wilder
12/8/2023 07:35:04 am
Rereading things again...the light came on this morning as this is an OR statement but, as always, feel free to correct me...it's still early in the day. I've been lucky and not had to utilize it much other than some canopies.
Reply
Eric R
12/8/2023 09:22:41 am
Dan,
Reply
sean
12/31/2023 11:12:25 pm
the adjacent hazard option only works when the resulting flow is equal to or greater than density * area
Dave
12/8/2023 11:35:31 am
Yep, and the 2019 Handbook commentary says these sections "were added in 2013 to provide an alternative...as opposed to having to calculate a full design area....in response to concerns with calculation areas that crossed boundaries between hazard areas sometimes containing sprinklers having different orifice size.
Reply
sean
12/31/2023 11:13:14 pm
i think this was added to add clarity as some were treating it two different ways
Alex
12/8/2023 08:46:31 am
This has happened multiple times now where I am going to be submitting a drawing and this forum makes a post that has me changing my design! Thank you for whoever posted the original comment and everyone's feedback. This has caused me to increase my main to a second floor awning.
Reply
Nick
12/8/2023 08:59:06 am
To be honest, I have yet to apply this rule but my understanding is that you would in way need to apply both rules and adjust based on the result of your calculations.
Reply
sean
12/31/2023 11:14:14 pm
my example that this comes up is spray booths
Reply
Dave
12/8/2023 11:24:20 am
In this Reliable webinar about changes to the 2022 edition of NFPA 13, Cary talks about the change / correction of the point o connection at about 1:18:30. The whole thing is worth a listen.
Reply
Thomas
2/19/2024 08:46:30 am
Would 2022 edition of NFPA 13; 28.2.4.2.5 apply to a very small outside loading dock?
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |