We're designing an 8,000sf gymnasium addition to an existing fully wet sprinkled single story 100,000 sqft elementary school.
I'm putting together the design build criteria for the fire suppression system for the addition. What determines if I can tie into the existing system to feed the addition? There are 2-1/2" and 3" lines nearby serving the existing gymnasiums. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Pete H
11/12/2021 06:47:35 am
A number of things, the first one I'd look at is making sure the 8,000 additional square feet doesn't take the existing systems over the protection area limitations outlined in NFPA 13 (2016 ed.) 8.2. and 8.2.1.
Reply
Dan Wilder
11/12/2021 06:58:44 am
Without any more details, short answer: When the hydraulics allow you to and from whichever system doesn't exceed the 52K limit. You can add onto any system at any point as long as you can prove it (square footage not withstanding).
Reply
Alex
11/12/2021 07:02:14 am
Hi,
Reply
Glenn Berger
11/12/2021 08:49:17 am
In addition to the above responses ensure that a new hydrant flow test gets conducted.
Reply
Jesse
11/12/2021 09:06:56 am
There are a lot of factors to consider.
Reply
Jack G
11/12/2021 09:23:18 am
You have to watch the “ fire alarm zoning” also. The addition may need to be in its own zone for detectors. If so, you may need system #3 .
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |