Is there a threshold of percentage-opening that would allow sprinklers to be omitted below a grill or something similar - like a metal grated catwalk?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Dan Wilder
2/9/2024 06:38:17 am
13-19' - 9.3.10 allows omission of sprinklers below ceilings where the opening is at least 1/4" wide, the depth does not exceed the width of the open space, and the overall opening is at least 70% and there are minimum clearances from the ceiling to the sprinklers above based on sprinkler spacing.
Reply
Anthony
2/9/2024 08:47:20 am
As Dan correctly state if its over 48'' wide you need to have sprinklers protection under any metal grate.
Reply
Dave
2/9/2024 10:21:49 am
I agree. I've also seen an informal NFSA interpretation stating the same, for reasoning including what Anthony states. Unfortunately, a grated walkway does not equal an eggcrate ceiling.
Jesse
2/9/2024 08:41:42 am
Agree with Dan's response. The percentage of opening you referred to originally deals with things like slatted ceilings and such.
Reply
Jack G
2/9/2024 09:39:16 am
I’m with Anthony.
Reply
Casey Milhorn
2/9/2024 06:39:48 pm
NFPA has a research foundation that did some recent testing on grated mezzanines and walkways. Very interesting findings and the affect on distribution and overall wetting was fun to see. If you have an AHJ open to making an independent ruling based on this research, you might look this research paper up, but as others stated NFPA 13 is very clear on needing protection above and below when over 48" in width.
Reply
Jim
2/14/2024 11:46:52 am
Do you have a link?
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |