What is the minimum design area for a deluge system?
NFPA 13 only specifies the design area for wet-pipe and dry-pipe systems. Is the design area the entire system? Many thanks! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Dan Wilder
11/16/2021 06:36:21 am
It depends.....not the greatest answer but as a general approach, you'll need to know what is being protected.
Reply
Anthony
11/16/2021 08:25:29 am
NFPA 13-2016 23.5 Says to see a different standard.
Reply
CJ Bonczyk
11/16/2021 09:07:05 am
As Dan has stated above it will depend on the occupancy and what the system is protecting. Deluge valves are used in preaction, open head, nozzle type, monitor nozzle systems, foam, etc.
Reply
Jesse
11/16/2021 09:30:46 am
It depends. And I'm presuming this is an open-head deluge system.
Reply
Franck
11/16/2021 10:10:00 am
The minimum area is the entire system controlled by one deluge valve. As all heads are open, you cannot consider the discharge of only a portion of them.
Reply
Jack G
11/16/2021 01:46:41 pm
Yes—- open heads, entire system or systems.
Reply
Alex
11/17/2021 06:00:14 am
Minimum area would be any heads assumed to open during a fire. Therefor, if your heads are open, calculate the entire system. For multiple systems, see NFPA 15
Reply
sean
12/31/2021 06:48:36 pm
all of them
Reply
Omar
1/8/2024 07:52:22 am
According to NFPA 16, section 7.3.7 : for foam water wet pipe , dry pipe and preaction system the total design area shall be 5000 ft2 (465m2).
Reply
rina
4/1/2024 07:57:05 pm
May I know why the deluge system is a must 7 psi?
Reply