Are you required to to laterally brace a pipe rise over 4-ft long to an upright, even though there is a horizontal break with a hanger? Is the vertical rise of pipe, before the break, considered a sprig or is the vertical pipe that feeds directly to the head considered the sprig? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
JI
10/28/2022 08:15:59 am
I would consider the vertical pipe before the sprig a riser, and it would require a hanger within 2'-0" of the riser as per NFPA 13 2013 9.2.5. Some lateral stability will be given from a hanger as per this code.
Reply
Dan Wilder
10/28/2022 08:39:51 am
NFPA 13 defines a Sprig as "A pipe that rises vertically and supplies a single sprinkler".
Reply
Chris
11/1/2022 02:30:14 pm
I would say since the vertical piece is not technically a sprig a hanger like the illustration shows would work.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |