Does the requirement in NFPA 13 that “All valves controlling water supplies for sprinkler systems or portions thereof, including floor control valves, should be accessible to authorized persons during emergencies. Permanent ladders, clamped treads on risers, chain-operated hand wheels, or other accepted means should be provided where necessary” imply there is a maximum height limit for floor control valves or standpipe isolation valves?
I have a couple standpipe projects where I am having trouble squeezing in a standpipe isolation valve down low (in elevation). I haven't found a confirmation in the standard or handbook that identifies a maximum height for accessibility. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Dan Wilder
2/14/2022 07:45:33 am
There isn't a set height....there may be " above 7' " rule of thumb (because anything below 7' becomes an egress issue).
Reply
Alex
2/14/2022 08:06:31 am
I agree with Dan above. You will often see isolation valves located above an ACT. If you have a gyp ceiling, you would need to provide an access panel. I would confirm with the AHJ that maintenance or fire personnel can utilize an A frame ladder to reach the valve.
Reply
Jesse
2/14/2022 08:07:00 am
You won't find a specification in 13 or 14 above "accessible".
Reply
Casey Milhorn
2/14/2022 09:02:15 am
Everyone pretty much covered it. I would add that I think it's vague on purpose. it can be a real balancing act to keep valves accessible but also out of harms way (free from mechanical damage, vandalism, etc.). This is a great example of where the standards don't, and shouldn't dictate everything in black and white. We have so many intelligent designers, engineers, and AHJs in this business and there is nothing wrong with them making decisions (together) on their projects.
Reply
Franck
2/14/2022 10:08:28 am
As I am not an English spoken language native, I often don't try to find many interpretations to a word and go straight to the point. And NFPA often does the same.
Reply
Jack G
2/14/2022 02:32:10 pm
Egress height will determine accessibility, I ve found in my 57 years.
Reply
Cesar Flores
2/14/2022 07:58:18 pm
In California code it those specified that they have to be at 7-0. All control valve , drain,check valve. Its only on NFPA 13. Nothing on NFPA 14. In the city off LA it those specified it on the installation manual.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |