I am working on a project with a new client who develops multi-level Self Storage Facilities.
The typical units are 10'x20' with 8-ft bent metal purlin dividing walls. The walls do not extend to the ceiling deck which is 11'-6" above finished floor. All sorts of household items are being stored, which can include exposed expanded foam mattresses that are greater than 5-ft in height when on their side. The tenants are limited in storage height to 8-ft because of 14 gauge metal wire netting above the units. On previous projects the client has been permitted to classify the hazard as OH2 (possibly because of the definition in NFPA 13, 5.3.2. 2016 edition, which includes contents with high-heat release rates up to 8-ft). The question is whether or not it should be Extra Hazard Group 1 or Extra Hazard Group 2? I am leaning towards EH1. The occupancy is a storage facility so I believe we fall into Chapter 12 for our design requirements. Because we have exposed expanded plastics stored greater than 5-ft we cannot be considered Low-Piled (Chapter 13). Therefore we fall into Chapter 15. Using NFPA13 Table 15.2.2.5(a) and the decision tree, selecting plastic commodities, Group A, Expanded, Exposed, Unstable, I believe the Density would be 0.30 gpm/sqft. This would be EH1. I am using NFPA13, 2016 edition. Can anyone speak to how they would classify the hazard (design area and density) for this type of storage facility? Should it be OH2, EH1 or EH2? Thank you. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
20 Comments
Pete H
4/10/2023 07:47:55 am
EH1 sounds right based on 15.2.2.5(a). Unless they put in shelves (no more than 8'-0" for top of storage) to make it "stable", then you can get down to OH2.
Reply
Glenn Berger
4/10/2023 08:19:31 am
The challenge with self-storage facilities is that no one will be policing the actual materials being stored, the actual storage arrangement, etc.
Reply
Jesse
4/10/2023 08:28:33 am
We do a lot of these and always design to OH 2 considering it to be misc. storage.
Reply
James Phifer
4/10/2023 08:59:42 am
we've completed about a dozen of these self-storage buildings in the last 10 years and have also always used OH 2, miscellaneous storage as the hazard classification. This has always been acceptable to our AHJ, the State Fire Marshal's office.
Reply
Eric R
4/10/2023 09:22:36 am
I'll preface this with it's entirely possible that OH2 is more than adequate for this hazard. I don't have any real-life data to argue that it's not.
Reply
Just an AHJ
4/10/2023 09:38:11 am
Great points in this reply. Your AHJ will probably prefer OH1 but I understand the need to win the bid to get the job in the first place. I think it's important to consider how people "organize" things in these storage units. As in...they don't. And they overload them and mix different hazards without a second thought. Someone may very well throw a mattress over the top of an entire unit full of random objects. They fire may be able to grow in size and intensity quickly while the water is blocked by a mattress, tarps, couch, etc. In my opinion it's better to be safer and assume the worst given the element of the unknown items and arrangement to be stored.
James Phifer
4/10/2023 09:47:25 am
I agree with you Eric. we really have no way of knowing what will be stored, in what quantity or in what manner. However, mattresses stored up to 8 ft would still be considered OH2. Since the storage isn't monitored well, we could still get into EH 1 or 2. but as you stated, my competitors aren't going to bid it that way. This needs to be stated by the EOR that they want extra hazard. I'd love to see more testing on this area.
Karl Beck
4/13/2023 08:04:43 am
Excellent post Eric. Regarding the allowable reductions to reduce pipe sizes. At the contractor/designer level, as you know, our job is to provide a compliant system in the most profitable way (not that this all is about money - but I guess it is!). That is why from an engineering (design professional) level, I feel it is important & have always been an advocate of providing (accurate) pipe sizes on bid documents. This levels the playing field for the bidders, and can save a building owner a ton grief. I have always been directed to design these types of storage units as an OH2, but based on your input, I can agree that an EH1 should, at least, be considered. Thank you for your excellent post!
Alex
4/10/2023 08:29:07 am
It seems appropriate to classify the hazard as Extra Hazard Group 1. As you mentioned, since the storage facility has exposed expanded plastic commodities greater than 5-ft in height, it cannot be considered Low-Piled (Chapter 13) and thus falls into Chapter 15.
Reply
Eric R
4/10/2023 08:43:10 am
My quick answer is that EH1 is what I've been using recently for similar projects. I've got three such buildings currently under construction at EH1 using the same code path you described, and all were well received by the AHJs when presented.
Reply
Carson B
4/10/2023 12:01:43 pm
I'm in agreement. I think it should be EH1. As mentioned by others, it boils down to money and bids.
Reply
Casey Milhorn
4/10/2023 09:15:23 am
We see OH2 almost every single time from the EOR. I would love for NFPA or FM to perform some testing and a study on this. I think ceiling heights and construction type play a huge role in this. Most of the conditioned mutli-level stuff we see has approx. 10' to 11' deck heights, and typically mesh installed at 8' to limit the storage height. I would have to imagine that activation is going to happen very quickly and uniformly over the areas with heat release. I'm no expert, but I would have a hard time believing that the area would involve more than a few 10x10 units (so maybe 300 sqft). To go to EH we are talking (25) 10x10 units being involved which seems very unlikely. Construction type is almost always metal skinned walls to 8' or 9', C channel metal construction for walls and supports, and concrete. A lot of the data in the storage sections of NFPA 13 is derived from storage with deck heights much higher than 10'+/-.
Reply
Dan Wilder
4/10/2023 09:17:06 am
The last couple we have bid, we bid for EH1 with an alternate to lower to OHII with AHJ approval (typically an owner's letter).
Reply
Zack H
4/10/2023 09:38:36 am
I did one of these recently and made an assumption that why mattresses are Group A expanded that mattresses and other expanded plastics were likely to be less than 25% of the total commodities. So, per Figure 5.6.3.3.3 (b) you would be able to still classify the commodity as Group A unexpanded. This would then move you to column A of Table 15.2.2.5 (a) and a .2/2500 density. Our AHJ was happy with this approach considering that they were typically approving OH2 in the past.
Reply
Carson B
4/10/2023 12:40:22 pm
This is very good, and a strong argument to go with OH2 - 0.2/2500 density. It may actually prevent the need for a fire pump in some scenarios where the municipal water has low pressure.
Reply
Carson B
4/10/2023 03:10:23 pm
After looking at Chapter 5 of NFPA 13 (2016) for a bit, I dont believe we can classify the "fire area" based on percentage of commodity types.
Reply
Eric R
4/10/2023 10:16:17 am
To add one more bit of complexity to the discussion.
Reply
Anthony
4/11/2023 07:11:12 am
Just another thought to the OH2 Vs EH1. The walls between each unit could be cinderblock and have an effective 2 hr rating or could be corrugated metal with no rating. That may help you choose between the 2 solutions.
Reply
James Art, FPE
4/12/2023 11:39:45 am
NOT in California:
Reply
Casey Milhorn
4/12/2023 07:33:21 pm
The intent of the reduced area was to encourage the use of QR sprinklers in OH hazards. Light hazard was just a logical beneficiary of this reduced area rule.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |