We are pressure testing a sprinkler system but there is no water available.
How much air pressure should be used to equal a 200 psi hydro test? Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
12 Comments
Mike L
6/24/2020 07:20:12 am
40 psi is typically used for air testing.
Reply
sean
6/24/2020 07:11:56 pm
it also says to go through with water testing when weather or conditions allow
Reply
Dan Wilder
6/24/2020 08:26:25 am
TL:DR - DON'T. Find a garden hose, rent a water truck, but NEVER fill a sprinkler system to 200PSI of air pressure.
Reply
Jonathan Sullivan
6/24/2020 10:14:08 am
Interesting aside, this is recognized by other model codes such as IPC. Air tests are prohibited for PVC piping, and if an air test is performed on drain and waste piping, it can't exceed 5 PSI, where if a water test were performed on the entire system, multi-story stack pressure could be many times greater.
Reply
Micheal
6/24/2020 10:17:09 am
I too echo the advice the advice. Considerable damage and even death may result from an air test at the pressures mentioned above.
Reply
HJ
6/24/2020 10:25:14 am
Do NOT pump up that wet system with air, for all the reasons listed by Dan Wilder. Even if you were to pump air into that system, it doesn't count-- you would still have to perform the hydrostatic test afterwards. Wait for your APPROVED water source to become available for your system.
Reply
Jonathan Joseph
6/24/2020 12:18:38 pm
Have the GC supply the water truck. In most contracts this is an Item that usually gets addressed and typically GC is responsible for supplying water for testing when the tap to a city main, private well or pond is not present.
Reply
6/24/2020 02:27:46 pm
I could not agree more. When one has a failure with high air pressure it is basically an uncontrolled explosion. This would lead to property damage and possible loss of life. Should chose to do it anyway. Please give advanced notice so that I can arrange to be out of town,
Reply
Cliff S
6/25/2020 10:09:52 am
Word of caution on air testing. Depending on the size of your system and the amount of noise on your project, it could be very difficult to find an air leak.
Reply
6/29/2020 07:44:08 am
A little bit of peppermint oil in the air intake works wonders in high noise environments .
Reply
Vahe Zohrabian
6/27/2020 12:54:28 pm
Agreed with all points above plus, Viscosity and surface tension of water is greater than that of air, about 89 times, and that viscosity, internal friction of water making it resist the tendency to flow, particularly through a small opening.
Reply
Vahe Zohrabian
6/27/2020 01:00:07 pm
Below you will find more information,
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |