I have a project which requires a water curtain be installed on both sides of the glass due to it being the wall down a corridor.
My questions are - (1) does this type coverage require a valve and separate pipe network or can it come off the base building wet system branch lines? Also, can these same sprinklers be used to cover the corridor as well? NFPA-13 Section 11.3 doesn't spell this out, so I'm not sure. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Mike L
2/25/2022 07:06:09 am
The closely spaced sprinklers providing the water curtain do not need to be on their own main. They can be connected to branch piping. However, it is recommended to put them on their own branch line to make the hydraulic calculations (balancing) a little easier.
Reply
Alex
2/25/2022 08:45:18 am
I think Mike spelt this out perfectly. The system can be feed off of the floor system but it will make it more challenging when balancing the system. With how advanced design software is now, I would say feed directly off of the floors system.
Reply
Travis Mack
2/25/2022 08:08:02 am
Are you needing to provide an alternative to rating the glass? If so, you will need to use the specially listed window sprinklers. They are not cheap. Standard spray sprinklers at 6' on center are not an alternative to using rated glass. You must use the specially listed ones if that is the desired result.
Reply
Jesse
2/25/2022 08:09:02 am
Window protection sprinklers do not need to be fed by a separate system. However, the design requirements are different than normal ceiling level sprinklers. Read the listing and equipment data sheet thoroughly. There are some architectural design considerations that are a pre-requisite for protecting glazing this way.
Reply
Franck
2/25/2022 08:09:05 am
As indicated by Mike, it is a good practice to have a separate system.
Reply
Todd Wyatt
2/25/2022 08:13:06 am
I recommend you review "Windows, Sprinklers, & Fire Ratings" (https://www.meyerfire.com/blog/windows-sprinklers-fire-ratings-part-i) to verify this "deluge" automatic sprinkler system meets the requirements of the applicable IBC edition and if it has been approved by the AHJ.
Reply
Glenn Berger
2/25/2022 09:07:51 am
Jumping on the bandwagon - Mike L. nailed it.
Reply
Casey Milhorn
2/25/2022 09:24:34 am
As Todd said, check out Meyers blog. I haven't read it yet, but I'm sure he covers everything very well.
Reply
Dave
2/25/2022 11:11:48 am
All correct - It gets very complex, and they must be calculated with the adjacent sprinklers. Even the glass itself has to be specific type and thickness, as well as the frames, size of glass (due to limitations of the size of furnace used in testing), combustibles must be heald away from the glass. Along with MeyerFire there are other good resources I keep on hand for each time I have to revisit the topic, including Sprinkler Age https://sprinklerage.com/window-sprinkler-design/ and Reliable's recent webinar from December 2020 https://www.reliablesprinkler.com/resources/webcasts/
Reply
What you're referring to are window sprinklers, not water curtain sprinklers.
Reply
Matthew Willis
3/9/2022 09:02:45 am
Just wanted to jump in and add..,
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |