We have to provide sprinklers 4 feet on center to protect the opening between a commercial kitchen and a seating area.
The number of heads to be calculated is based on the 1.2 times the square root of 1500 per NFPA 13 2007 Edition. W have first calculated the water curtain demand assuming each sprinkler needs to flow 15 gpm. We get a required pressure and flow for the end node serving the water curtain. The calculated flow/pressure is then used in the full calc to balance the remaining system around. So in essence we are calculating the system in two parts. Is this the correct methodology? As best I can tell the water curtain demand must be in addition and must be balanced with the remote area. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments
Rusty Scott
7/16/2019 10:27:30 am
Out of curiosity because I'm doing my first water curtain system in the near future, what type of sprinkler heads are you using? I've seen specific water curtain type heads from out of US companies and I've done some light reading that you can use pendent or vertical sidewall type on horizontal as well. Not sure what's true or preferred method, any thoughts?
Reply
Wayne Ammons
7/16/2019 12:00:29 pm
These are specific application window sprinklers and are specifically listed for the purpose of protecting glazing. They have a different intent than sprinklers used for the purposes of providing a water curtain. Standard spray sprinklers can be used for a water curtain.
Pari
7/16/2019 10:27:57 am
If space between sprinkler is 4 feet , baffles required.
Reply
Mike
7/16/2019 11:33:10 am
11.3.3.1 Sprinklers in a water curtain such as described in
Reply
K.T.Daniel Raj
6/5/2021 07:23:29 am
We are considered arround -500 water curtain .. what's pumps required.. kindly give me suggestions..
Reply
Joel Mathew
11/10/2022 03:08:27 pm
What code or NFPA section is this requirement for the protection between kitchen and seating from?
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |