Hi all, I need help on this one:
There is a floor space in between the roof and the top story of a building. It's non-combustible construction. The floor space in-between the roof and top story is 13-ft (4 m) high with limited access, about 64,000 sqft (6,000 m²) in floor area, no occupancy or storage intended, only pipes and ducts will be in this space and the equipment will be at roof level. The architects refer to this as a concealed space. 1. Can this be considered a concealed space? 2. Are there any limitations for concealed space in terms of size? 3. Does this space requires sprinklers? Any suggestions will be highly appreciated. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments
Glenn Berger
9/26/2022 08:14:58 am
Your question said "limited-access," "floor space" and "no occupancy or storage intended." These are buzz words trying to skirt code requirements. My gut reaction is that during the life of this facility, this space will be used and therefore sprinklers should be installed at this time.
Reply
Jesse
9/26/2022 08:19:11 am
I missed the "limited access" part. Access changes this for me and I agree with Glenn's assessment. I think it should be protected.
Reply
Alex
9/26/2022 09:13:17 am
Glenn hit the big points here. I would be nervous based solely on the language used in the question here. I would confirm it is truly meant to be a congealed space before omitting sprinklers.
Simon
9/28/2022 11:12:28 am
Hi Glenn,
Reply
Greg
9/26/2022 08:16:00 am
I have seen this type of space in differing configurations; solid floor with drains, grated suspended floor over ceiling tile, and truss supported floor decking.
Reply
Greg
9/26/2022 08:29:56 am
I did forget to mention, on the chance it is a grated suspended floor over ceiling tiles and the space below the tiles is an assembly occupancy or any populated occupancy .... and assuming you do install sprinklers, what is the result of a fire even where one sprinkler actuates , and subsequent alarm (up to 60 seconds) , in regards to the safety of people below from saturated ceiling tiles.
Reply
Jesse
9/26/2022 08:16:54 am
Well, it is a concealed space by definition. However, I don't see this a combustible concealed space unless building equipment in that space is combustible. Its not different from a non-combustible buildout in a large shell building where we may protect the office occupancy below but not the area above.
Reply
Jesse
9/26/2022 08:17:58 am
I think I missed the "limited access" part. How limited is the "limited" access??
Reply
Simon
9/28/2022 10:49:54 am
There are a couple of 2x2 hatches accessible from the roof above, my guess is that they have these for service. I don't think there is any possibility they use this space for storage. From the roof to the floor space is 13 ft high. No other access points from the floor below. 9/26/2022 08:25:48 am
NFPA 13 - 2013 Chapter 8/8.15 Special Situations
Reply
Dan Wilder
9/26/2022 08:26:21 am
If it meets the requirements of 13-19' 9.2.1 for concealed spaces, sprinkler omission is allowable. No to any footage maximums (in square feet or cubic feet) that I am aware of.
Reply
Steven
9/26/2022 09:01:06 am
As others said, I would find it hard to believe that such a large space would not be used for storage or some other occupancy at some point down the road. Of course, adding sprinklers to this area will be a very costly change to the customer, and it's difficult to justify such a change based on only our intuition. I don't know if there are any code references that would explicitly indicate that this area is too large to be considered a concealed space. As such, I think it would be good to discuss with the AHJ to get something "official" which can be used to justify why sprinklers should be added (which is what I think will be what they request).
Reply
Todd E Wyatt
9/26/2022 09:58:23 am
2021 IBC would define this space/area as an “ATTIC” (and the AHJ may agree) …
Reply
Franck
9/26/2022 10:21:06 am
As confirmed by others, this is a concealed space (or unoccupied floor, whatever you want to call it) and it does apparently not require a sprinkler protection now. But on the long term ? I have seldom seen such nice “empty” spaces, out of sight, remain empty for a long time.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |