Can I install a concentric reducer in the vertical position and a 90 on the suction side of a vertical inline pump?
The feed is coming from above the pump, and we don't have space for a 90 and an eccentric reducer. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
JohnF
7/14/2021 08:08:59 am
use a reducing elbow
Reply
schulman
7/14/2021 08:11:24 am
NFPA 20 has some pretty good diagrams of the dimensional requirements for distance from fittings and orientation of fittings leading into the suction side of a pump. You should be able to find info that informs on your situation ...
Reply
Casey Milhorn
7/14/2021 08:30:03 am
I've done it before and I can't think of any restrictions for this scenario. but as Schulman said, NFPA 20 is fairly clear on fittings and dimensions.
Reply
Jesse
7/14/2021 08:30:24 am
Look at the annex material in NFPA 20. I think its A4 or somewhere there.
Reply
Glenn Berger
7/14/2021 09:05:26 am
4.16.6.4 requires the use of eccentric reducer where the suction pipe and pump suction flange are not of the same size.
Reply
Jay
7/14/2021 09:13:09 am
2019 NFPA20: 4.16.6.4 Eccentric Tapered Reducer or Increaser.
Reply
Craig S
7/14/2021 09:35:53 am
Like others have said, you should be using an eccentric reducer per NFPA 20, 2013, 4.14.6.4. As far as I am aware, eccentric and concentric reducers are the same length, so you should be fine there. Vic's #50 and #51 are both the same length, I would assume other manufacturers would be the same.
Reply
Franck
7/14/2021 11:05:05 am
That's an interesting configuration (never met so far).
Reply
Jay Richardson
7/14/2021 11:54:06 am
In regards to: If you want a better laminar flow, to limit cavitation, I would suggest to put the reduction as far as possible from your elbow.
Reply
Peter
7/14/2021 03:39:47 pm
This was my thinking as well. NFPA 20 requires 2 things: (1) certain pipe size 10 suction diameters upstream of the pump and (2) that you use an eccentric reducer for sizes that aren't the same from the pump suction flange to the suction piping. If your suction piping needs to be 6" (say a 750GPM pump), adding a 4" or 5" 90 degree elbow connected to the suction flange wouldn't meet the intent of 4.16.3.3. Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |