I am an architect and appreciate the information being shared here, very clear and helpful. We are working on an atrium and working in accordance the Closely-Spaced Sprinklers (for Atrium Enclosures).
In the details for the closely spaced sprinklers there is a horizontal distance of 4-12" from the glazing to the sprinkler - is there a separate vertical dimension that must be met? We have glass that is 11'-4" in an open/exposed ceiling that is 13'-5" high (at boundary of atrium). Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
6 Comments
Wayne Ammons
4/7/2020 07:50:59 am
Is the intended use of the closely spaced sprinklers to provide glazing protection to achieve a fire rating? Can you reference what code and section the details you are looking at are from?
Reply
Keith Heckler
4/7/2020 10:12:18 am
Contact me directly and I can share with you photographic arrangements found through North America to help you see other installations. keith.heckler@fema.dhs.gov
Reply
Greg
4/7/2020 10:31:47 am
Hi, I am a MEP engineer. Appreciated if you could enlighten me if NFPA and FM Global asking for standby fire pump to be an engine-driven pump. From my reading of the standards, I couldn't find the statement. However, there are many senior staffs and clients keep telling me that if the fire protection system to comply with NFPA or FM Global, then an engine-driven pump is required for standby.
Reply
sean
4/7/2020 04:16:37 pm
Not counting insurance requirements NFPA 20 talks about 2 different reasons to require a pump to have a secondary power source (day tank w/ refill contract, ATS and generator, etc.).
Reply
Mike
4/7/2020 10:36:05 am
Tyco and Reliable have window sprinklers. It's best to check their data sheets.
Reply
sean
4/7/2020 04:17:51 pm
the MFG requirements and the ES report cover both. Make sure you read both as they sometimes are on different revisions.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |