Can I use a horizontal sidewall fire sprinkler (not a dry horizontal sidewall) in cold rooms where there is risk of freezing?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments
Alex
8/10/2021 06:33:27 am
Hi Anonymous,
Reply
Alex
8/10/2021 07:00:09 am
My apologizes, I have a type-o in my response. I meant, if you have a wet sprinkler system, you can look into a dry barrel sprinkler.
Reply
Dan Wilder
8/10/2021 08:28:51 am
With that revision/clarification, yes and it occurs frequently.
Jake
9/14/2021 04:56:53 am
Hi! thanks for your comment. I forgot to tell that the system is dry sprinkler system. Ive seen normal sprinklers in dry systems in cold places like car parks outside a mall.
Reply
Jeremy
8/10/2021 08:07:48 am
Any where that the temperature is subject to dropping below 40°F, should have a dry barrel sprinkler.
Reply
schulman
8/10/2021 08:16:25 am
just in case you need one more vote ...
Reply
Glenn Berger
8/10/2021 08:30:24 am
Too risky to use a standard sidewall. Use dry sidewall with a length to ensure that the water is not close to the cold perimeter of the room.
Reply
Taylor Schumacher
8/10/2021 08:36:51 am
You may use a sidewall in that area if it is fed from a dry-system.
Reply
Jake
9/16/2021 06:39:34 am
Yep, its fed from a dry system. sorry i forgot to include this fact in my question.. is there a rule about this situation in NFPA 13?
Reply
Alex
9/16/2021 07:30:58 am
Jake,
Jesse
8/10/2021 08:43:02 am
No, you can't.
Reply
Mike
8/10/2021 08:44:45 am
If you use the dry barrel, don't forget to use a tee with a plug.
Reply
DAVE
8/10/2021 10:42:05 am
And with a dry-barrel sprinkler, utilize the correct dry-barrel length according to exposed temperatures and seal the penetration openings appropriately.
Reply
John G.
8/10/2021 11:54:16 am
Sorry. Should be a no brainer. Did your designer " fall out of the turnip cart? "
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |