I have a project in the Miami area where there are some exterior glass panels that need to be 1-hour fire rated.
I specified the glass to be fire rated type, but it prices are coming back too high. The contractor is looking into an alternative of providing fire sprinkler protection on the inside face of the glass. Is this a feasible idea? The wall that the glass is part of requires the rating due to its being within 10' of some adjacent exterior glass. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Pete H
1/15/2024 06:36:09 am
Based on this handy dandy Meyer Fire write up, there's definitely some things that can be done, especially with Tyco WS sprinklers:
Reply
Dan Wilder
1/15/2024 07:05:35 am
If this is acting as an exposure type system with sprinklers on the exterior to protect your building from the adjacent building (possibly unsprinklered or already has the rated glass), you're looking at a deluge system. If it's just a separation between two sprinklered buildings, you can likely get the AHJ to approve interior closed WS on your building only. If it's the same building with some large architectural inset(s), interior sprinklers should be acceptable as well.
Reply
DE
1/15/2024 08:08:11 am
Exactly what Dan said. Make sure the glazing & mullions conform to the WS requirements if you go that route.. there's quite a few. Check the data sheets.
Reply
Jim Stever
1/15/2024 08:08:08 am
Agree with above comments. However, what happens when the fire sprinkler system is down. I would still use rated glazing
Reply
Glenn Berger
1/15/2024 08:54:40 am
Dan laid out the thought process exactly correct. Depending on the occupancies and the hazards that are present will advise which is the right way to go.
Reply
Matthew Signes
1/15/2024 08:55:04 am
Victaulic also has a Specific Application Window Sprinkler solution.
Reply
Dan Wilder
1/15/2024 04:11:07 pm
Good call....haven't tried them!
Reply
Jesse
1/15/2024 10:09:52 am
Yep, we've encountered this on numerous projects due to the price of rated glass. There are numerous window protection sprinklers on the market. Just make sure the sprinkler you choose is listed for such use.
Reply
Casey Milhorn
1/15/2024 12:55:56 pm
Agree with Dan. Make sure that you follow the listing of the head and/or if using SS heads (when allowed by applicable codes, AHJ, etc) follow IBC/IFC and NFPA 13 standard.
Reply
Ivan Humberson
1/16/2024 11:19:32 am
You will definitely want to check with the AHJ to work toward a solution. If the jurisdiction enforces NFPA standards, then, to my knowledge, there is no NFPA compliant alternative to a 1-hour assembly that allows sprinkler-protected glazed openings.
Reply
Todd E Wyatt
1/22/2024 03:49:20 pm
“Water curtains” are permitted to be substituted for fire-resistance rated (FRR) opening protectives in buildings protected throughout by an automated sprinkler system (ASPS) by the scoping Code (e.g. IBC-2021 705.8.2) if approved by the AHJ (e.g. Building Official).
Reply
Todd E Wyatt
1/22/2024 03:49:52 pm
REFERENCES
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |