I would appreciate some feedback on using quick response sprinklers in a dry system. I have found no reference in NFPA 13 indicating specifically if QR Uprights can or can not be used. Therefore, I assume that they are acceptable providing it is a light or ordinary hazard classification.
I have researched and found varying opinions. I believe fire testing shows that the use of QR sprinklers in dry systems can help decrease fluid delivery time. However, with more sprinklers operating before the water arrives to control the fire, some argue that there is increased system demand. I agree with both scenarios, however, I don't believe the amount of sprinklers operating would exceed the design area of a properly calculated system. I would love to hear some different opinions on the subject. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments
Thomas Jones III
1/8/2020 10:08:52 am
QR are allowed for dry systems and actually are required per NPFA 13 (2010) 8.3.3.1, if you dry system protects a light hazard area.
Reply
Mike L
1/8/2020 01:44:58 pm
Sprinkler RTI (fast response vs standard response) and water delivery time are two totally separate items.
Reply
B.P.
1/8/2020 05:01:28 pm
Excellent answer! I believe NFSA did conduct full scale fire tests which suggested that quick response sprinklers, by nature, did activate quicker decreasing the delay in water delivery to the fire and consequently reducing overall ceiling temperature.
Reply
B.P.
1/8/2020 06:49:11 pm
Does anyone know definitively what FM recommends? I have heard discussion that they don’t recommend QR sprinklers in dry system installations but, have been unable to find anything in the data sheets.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |