A small core area of a two-story office building has two stairs. One is a traditional enclosed exit stair fire-rated at 1-hour. The other stair is intended to be an "open access stair". The project is under NFPA 101 for means of egress and is sprinkler protected under NFPA 13.
NFPA 101 Chapter 38 New Business Occupancies NFPA 101 38.3 Protection NFPA 101 38.3.1 Protection of Vertical Openings NFPA 101 38.3.1.1 Vertical openings shall be enclosed or protected in accordance with Section 8.6, unless otherwise permitted by any of the following: (4) Exit access stairs in accordance with 38.2.4.6 shall permitted to be unenclosed. NFPA 101 38.2.4.6 A single means of egress shall be permitted for a maximum two-story, single-tenant space or building provided that both of the following criteria are met: (1) The building is protected throughout by an approved, supervised automatic sprinkler system in accordance with 9.7.1.1(1). (2) The total travel to the outside does not exceed 100 ft. The only way to have an unenclosed stair for this building is if the "total travel to the outside" can include travel through the unenclosed "exit access stair". Is it permissible to have one open stair and one enclosed stair with "total travel to the outside" going through the open access stair? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
2 Comments
Marc Vieno
12/10/2019 11:17:26 am
Since you have two means of egress, you should see if the space can meet one of the other options in 38.3.1. Unenclosed stairs are usually pretty easy in a business occupancy.
Reply
David Duffy
5/18/2023 11:04:59 pm
The description of the project notes "The project is under NFPA 101 for means of egress and is sprinkler protected under NFPA 13". The key here is "for means of egress" - which is common when paired with an IBC building code - and I am careful to distinguish between the two..
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |