We have scenario where we are using foam system under NFPA 11 for a floating roof tank with Crude Oil.
Based on our previous calculation for a prior tank the fire water demand is 1,926 gpm so we have existing 2,000 gpm pump to be able to supply the required flow. But an additional Crude Oil tank has been added and we have run our new hydraulic calculations and we come up with 4,496 gpm new flow requirement. Is there a way we can still use the existing fire pump? Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments
Dan Wilder
9/17/2020 10:52:38 am
The only way I see this working is if you setup the pumps in parallel. As the old pump works for the original remote area it's a matter of setting the second pump up for the correct "PSI ON" for sequencing along with the correct proportioner requirements
Reply
Brad K
9/17/2020 12:42:45 pm
I agree with the above. The suction sizing was my first concern for parallel pumps. Please consider the ID of suction pipe if HDPE pipe in play. This is a common issue.
Reply
Jon Dimanlig
9/17/2020 08:02:54 pm
Water source is coming from a Fire water storage tank. We are using a balance pressure pump proportioning foam system.
Reply
anthony brown
9/17/2020 01:39:37 pm
Some questions and some assumptions: I am assuming that this is a Wet System and that it is using low expansion foam. Is the Bladder Tank able to hold capacity, I'm assuming that it is sized for the existing system, and if I am reading your question correctly a new oil storage tank was added and that created the additional loading. final assumption is that you are supplying the system from a Municipal source i.e. "City Water".
Reply
Brett
9/17/2020 02:51:39 pm
What is the reason for simultaneous foam application on the two tanks? What is the separation distance between tanks? Most multi-tank farms are not designed for simultaneous foam application across all tanks. I would recommend speaking with the local AHJ to determine what their requirements will be before proceeding. The local fire departments operational procedures for response to the facility should be taken into account in the design.
Reply
SK
9/17/2020 04:40:04 pm
Certainly your new demand (4496 gpm) can not be met by existing Pump (2000 gpm) if scenario established to needing water/foam in both tanks together. The way I see with limited information which you provided, foam system for both tanks together probably not required in any scenario and other tank may need only water spray. It depends where you are applying foam whether it's for Seal RIM fire (external floating room) or for Dike protection. Please note that foam is ONLY meant to protect from pool fire scenario whether it's on roof or at ground. For Exposure/Cooling protection water spray system is required for adjacent tank (s) if these tanks are located downwind and affected by thermal radiation from "Tank on Fire". So in either the case, if foam applying for one tank, other will need water spray only. Water Spray can be limited to unwetted surface only for nearby tanks. Another scenario for crude tank fire is "Roof Lost Fully Involved Tank Fire" where you can not do anything for the "Tank on Fire" except watching helpless, you need to let that burn but your focus should be shifting to protect other adjacent tank(s) from heat exposure to avoid escalation. It is worth noting that "Roof Lost Fully Involved Tank Fire" is not credible scenario and failure frequencies for such scenario are very rare if tanks are complying API/ANSI requirement. However before I address your concerns more appropriately; appreciate following information;
Reply
Mike
9/17/2020 04:42:50 pm
I agree with Brett. Scenarios are based on one fire event. In my experience, if tanks are closer than 1 diameter cooling water is used on adjacent tanks. API 2030 and NFPA 15 are good references along with NFPA 30. Maybe a radiation study would be more revealing in actual risks.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |