Can a drum drip be used as a remote inspector's test for a sprinkler system?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Alex
11/1/2021 06:09:11 am
HI Anonymous,
Reply
Dan Wilder
11/1/2021 08:22:29 am
Yep, I do it a lot for odd systems but it typically means running the last branch line low or providing an additional 1" pipe that connects the main to the low point/inspector's test assembly. I will run out the same size branch line through the assembly and keep the discharge that same size.
Reply
Craig Hanson
11/1/2021 08:45:49 am
No, it cannot. The drum drip comes off the low point of the system for drainage [NFPA 13: 8.16.2.3.5*]. The inspectors test comes off the highest most remote piping [NFPA 13: 8.17.4.2.2]. 2 different animals.
Reply
11/1/2021 09:20:13 am
Craig, What edition of NFPA 13 are you referencing as I looked at 2010, 2013, 2016. 2019 does not have that reference. In each of the prior 3 editions it says in 8.17.4.2.2 "The test connection shall be accessible"
Reply
Craig Hanson
11/1/2021 09:37:21 am
2016:
sean
11/6/2021 07:36:21 am
A drum drip is a drain, you can have extra drain that also serves as a test location.
Reply
CJ
11/1/2021 09:43:10 am
I agree with Dan W. I have done that many times as well. Depending on the Fire Marshal they will allow you to combine the exterior discharge line with a site glass or will require two individual lines discharging separately. Always remember the only way this works is if this is the remote end of the system.
Reply
11/1/2021 09:48:36 am
Thanks Craig, turns out I was reading 2 versions of 2013 and not the 2016 book.
Reply
Craig Hanson
11/1/2021 10:08:38 am
I agree with Dan that it is done a lot and accepted by some AHJ's. However, It is not the best way to run an inspectors test and is by code, not the correct way. I was a fitter for years and we always ran separate lines for drains and inspector tests. Granted, we dealt with mostly pipe schedule systems and every bit of help to make the trip test was needed.
Reply
Franck
11/1/2021 04:05:26 pm
As indicated by Craig, it is quite often done… and accepted by some AHJ… but this does mean this is correct.
Reply
sean
11/6/2021 07:37:39 am
I would say you can build your remote test location as a drum drip, but it may not serve as the required aux. drains that are needed.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |