In a recent project, I asked for hydrant flow test results from the civil engineer, and I received Boundary Conditions instead.
Is there a way of using this information to validate hydraulic calculations? An example of Boundary Conditions given to us: Demand = 18.54 gpm (1.17 L/s), HGL = 463'-11" (141.41 m), Pressure = 64.1 psi (442 kPa). Thanks! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Dan Wilder
4/17/2024 07:16:43 am
These results look to have no direct correlation to information needed for a water supply (real life testing nor modeling) especially as to the volume.
Reply
Glenn Berger
4/17/2024 08:10:33 am
The numbers that you were given are not useful for a fire sprinkler system hydraulic calculations. A flow rate of 18.54 gpm may not be sufficient for a single sprinkler.
Reply
Jesse
4/17/2024 08:16:50 am
Ugggg, boundary conditions. My grandfather was a hog-farmer in the midwest and would utter something about it being as useful as some sort of sustenance appendage on a bore-hog blah blah blah.
Reply
Anthony
4/17/2024 08:17:07 am
NFPA 13-16
Reply
Ricardo Gonzales Jr
4/17/2024 08:59:29 am
What is not clear or may be me, is what is a 'Boundary Condition' as they describe it. As many of the previous answer indicate, the raw numbers appear useless as they don't describe the supply system in terms useable for Fire Protection.
Reply
Jack G
4/17/2024 09:45:21 am
Useless. In some of the states down on the east coast before you can build…. Anything, you must make a flow test and include it in the drawings and specifications, paid for by the building owner. If it takes longer than 6 months to build/ occupy, then another must be made for the CO. Makes it easy on contractors.
Reply
Anon
4/17/2024 10:39:29 am
I suggest confirming what is meant by "boundary condition." I see on the internets that term is used in describing aquifers, but also as describing a outer parameter of flow test, in which case that flow is useless for our purposes. Perhaps it is a regional term unfamiliar to many of us here.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |