Are we permitted to use the control valve on the backflow preventer as the system control valve?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Alex
8/6/2021 07:37:40 am
Hi Anonymous,
Reply
Jay Richardson
8/6/2021 04:39:53 pm
The control valves on the backflow are typically the only control valves on a single riser system, unless that single riser supplies a multiple story building with floor control valves.
Reply
James Phifer
8/6/2021 08:08:52 am
NFPA 13: (2016 ed ) 8.16.1.1.2.5 A listed backflow prevention assembly shall be permitted to be considered a control valve, provided both control valves are listed for fire protection system use and an additional control valve shall not be required.
Reply
Lary Morris
8/6/2021 08:24:14 am
Be sure the Water Department will allow you to 200 psi Hydrostatic Pressure test against that valve. For exemple St Petersburg Water dept Forbids pressure testing against The Backflow Valve.
Reply
Casey Milhorn
8/6/2021 08:46:03 am
Good point. I know as a company policy, we don't pressure test against any backflow (without closing the valves), and when flushing we either do it before the install of the DCVA or remove the internals when flushing.
Aaron
8/6/2021 08:21:30 am
I have employed this method in skidded fire pump assemblies (limited space inside) with no issues or AHJ objections.
Reply
CJ Bonczyk
8/6/2021 09:08:37 am
Yes you can per NFPA 13, however be sure to check with local water department requirements and your AHJ. Sometimes they may or may not allow items like this. For instance in a previous jurisdiction I lived we were required to use RPZ backflows, and the water department required an independent monitored control valve downstream.
Reply
John Galante
8/6/2021 03:25:58 pm
We always used what we called “ a frying pan “! Piece of sturdy metal, made with a “ handle” and bolt holes , tgat we’d drop between a pair of flanges for testing purposes . Whether a cut in, ( made with flanges to separate old from new) of bfp valve. Simple drop in and pull out .
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |