What is the required pressure for a manual Class III standpipe, 65 or 100 psi?
We're working on a 44'-4" high, 5-story, Type V-B construction building that has a 1-story garage and amenities. The upper floor is R-2. The local code says I can have Class III standpipe. As I go through NFPA 13 and NFPA 14, it circles back around to 2-1/2" outlets, except with 2-1/2" x 1-1/2" reducers and caps. It's going to be fully-sprinklered with a combination standpipe in one stairwell, and just one standpipe riser in the other. Does this sound correct given the project? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Dan Wilder
9/26/2023 08:14:45 am
IFC 2021 - 905.3.1 requires the Class III based on your description (4 or more stories above grade, Floor level on highest story is greater than 30' above lowest level of FD access), but allows Class I in fully sprinklered buildings when the hose lines will not be used by trained personnel or the FD (905.3.1 Exception 5). Any reference to standpipes out of this section references to NFPA 14 (905.2). Als, doesn't account for any local AHJ adoptions or modifications...
Reply
Danial Bartle
9/26/2023 09:53:42 am
Speaking as a retired firefighter, the "high-rise" hose packs usually have 1 1/2 or 1 3/4 hose preconnected to a nozzle, and a 2 1/2 x 1 1/2 (2) gated wye. The wye is connected to the standpipe and one line is used with the ability to add another 1 1/2 connection without stopping water flow. So generally up to 2 handlines per 2 1/12 connection.
Reply
kimberly olivas
10/2/2023 09:48:50 am
Thank you!
Reply
Glenn Berger
9/26/2023 08:39:57 am
Agree with Dan's responses above.
Reply
Jesse
9/26/2023 08:46:06 am
Agree with both Dan and Glenn. And yourcalc is 250-gpm @ 100-psis.
Reply
Casey Milhorn
9/26/2023 10:01:49 am
I agree with the responses and that a Class I standpipe, using Class III connections, is the most common method for standpipe design and install that I see (for non-high rise buildings). As Dan said, definitely talk to your local AHJ for any variances they have/want.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |